No, with Vertical Inline pumps the suction into the eye of the impeller is from 
one side (the bottom) to flow imbalances are not a critical factor. With 
Horizontal Split-case pumps the suction into the eye is form both sides so 
imbalances can cause uneven loads on the bearings and wear rings.

Richard L. Mote CET
Designer / Retired
 
 
-----Original Message-----
From: Brian Harris <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Mon, Nov 24, 2014 10:09 am
Subject: Vertical Inline Pump


NFPA-20 sets limitations on elbows & tee's with regard to horizontal split-case 
pumps, I don't see anything like that for vertical in-line pumps, am I missing 
something?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935