Interestingly, I just finished up a project on an oven where the owner's 
insurance company (FM Global) did not require sprinklers within the oven but 
the owner's customer did for business interruption reasons. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Dec 4, 2014, at 5:46 PM, Taylor, Galen <[email protected]> 
> wrote:
> 
> Art,
> 
> I have worked in the composites industry. It's a second career paralleling my 
> fire service. The vast majority of industrial ovens I've seen in the 
> composites industry have sprinklers. I'm surprised to hear that your clients 
> insurance rep does not think sprinklers are a good idea. Factory Mutual would 
> disagree based on the attached data sheet. NFPA 86 Standard for Ovens & 
> Furnaces advises sprinklers in accordance with NFPA 13.
> 
> One possible exception may be if the actual oven is physically outside the 
> building and the oven doors are incorporated into the building wall. But as I 
> always say too, Check with your local AHJ to get their take on the matter; 
> because at the end of the day it's what AHJ wants that counts.
> 
> Galen Taylor
> County of Los Angeles Fire Department
> Fire Prevention Engineering
> 323-890-4339
> [email protected]
> 
> "Ensuring Public Safety Through the Built Environment"
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Art Tiroly
> Sent: Thursday, December 04, 2014 1:05 PM
> To: [email protected]
> Subject: Curing oven for reinforced plastic tanks.
> 
> We designed a sprinkler system for a gas fired curing oven for plastic tanks 
> reinforced with carbon fiber and fiberglass.
> 
> The 10 - 40 gallon tanks hang from a conveyer. Zone temperatures vary from 
> warm to 200-250*F. Cure is over 24 hours.
> 
> We show about 20 sprinklers but the owner is reluctant to have sprinklers in 
> the oven and his insurance company agrees.
> 
> 
> 
> What say the forum.
> 
> 
> 
> Art Tiroly
> 
> ATCO Fire Protection/Tiroly
> 
> 24400 Highland Rd CLE 44143
> 
> 216-621-8899
> 
> 216-570-7030 cell
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to