"Hangar type is determined by features listed in NFPA 409 Article 4.1 not the 
IBC."  That is simply not true in the unamended IBC.  See IBC '12 412.4.6.  The 
only thing you use NFPA 409 for when coming out of IBC is "Aircraft hangars 
shall be provided with a fire suppression system designed in accordance with 
NFPA 409, based upon the classification for the hangar given in Table 412.4.6." 
 Also see IBC '12 101.4 Referenced codes. "The other codes listed in Sections 
101.4.1 through 101.4.6 and referenced elsewhere in this code shall be 
considered part of the requirements of this code to the prescribed EXTENT (not 
shouting just emphasizing) of each such reference."  The extent of reference to 
NFPA 409 is fire suppression, nothing else! 

"Usually Construction Type selected is Type II (000) (see NFPA 220)" You should 
not be seeing NFPA 220 coming out of IBC. I won't argue they are not nearly 
identical.  The point is use the right code properly. 

"which determine the easiest draft curtain locations/assembly and fire zones 
set off by the 75' circle."  Where does this 75' thing come from?  I don't see 
it.  In fact the '04 and '11 say 100' but this is for deluge systems not closed 
head systems as the OP originally stated. NFPA 409 '12 6.2.10.2.1 
...."Sufficient water supply requirements are determined by assuming that a 
fire at any point will operate all the systems in every draft-curtained area 
that is wholly or partially within a 30 m (100 ft) radius of that point 
measured horizontally."  Closed head systems in group I are 15,000 sq.ft. 
regardless of how many systems are within 75' or 100'.  If you are using draft 
curtains they are around each sprinkler system and subdivided so that the area 
bounded by the curtain (not the sprinkler system) is max 7,500 sq.ft.  The 
draft curtain location has nothing to do with how many systems or area to 
calculate. 

NFPA 409 is quite clear "7.6.2 The minimum discharge density shall be 0.16 
gpm/ft2 of foam solution over the entire storage and service area."  In this 
application the correct design area is 16,900 sq.ft., whether you have 2 
systems or 16,900 systems whether or not you have draft curtains. 

All of my comments are based on the unamended IBC.  Are there exceptions, sure. 
 FM being one of them, if insured by them you follow all of NFPA 409.  I have 
yet to find an amended version of IBC where 409 is brought in.  Even in places 
with NFPA 101 adopted you'd be hard pressed to get to all of 409.  Maybe if 
NFPA 1 or 5000 is adopted, I don't know because I've never work in a 
jurisdiction that did that. DoD you can't get to the full NFPA 409 either.  
Navy gets close though.    

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bob Holland
Sent: Tuesday, January 06, 2015 2:25 PM
To: [email protected]
Subject: RE: Foam & HangArs

Don,
No worries.  The misspelling happens a lot.  An older hangar guy drew me a 
picture of a commercial jet draped over a wire hanger once which made it 
memorable. 

In P&G's old hangar was the certification from the FAA.  On the single typed 
page hangar was spelled with an 'e' and an 'a'.  2009 IBC Commentary has it 
both ways in adjacent paragraphs.

I'd bet that guard's duty assignments did not improve.

I think pop ups were being used by the military a few years before the NFPA 
committee on 409 took it up.  We did our first 'public' version around 2005-6 
with the knowledge from these and a letter it would be included in the next 
edition.

Back to the original question.
And assuming you must use foam...
Hangar type is determined by features listed in NFPA 409 Article 4.1 not the 
IBC.
In the case of Group II, this determines construction type and minimum-maximum 
zones.
Usually Construction Type selected is Type II (000) (see NFPA 220)  because its 
unprotected steel - basically the old 2-C circa 1996.
Then the dance between footprint, aircraft parking/maneuvering, girt span 
capability, framing, door pockets and fire zones begins.  Start with aircraft 
requirements then to girt span (26-28' usually, outboard on cantilevered CMU 
stem walls), which determine the easiest draft curtain locations/assembly and 
fire zones set off by the 75' circle.  The goal is to shed zones using the 75' 
activation circle.

In other words, if your hangar was 130 x 130 and your bays front to back are 
26' wide, you have five zones and you only activate three at worst in any given 
scenario;  i.e. your supply/storage calcs need to accommodate coverage for 
10,140SF not the full 16,900SF cited below.

Hope this helps, Bob.

ROBERT HOLLAND Jr. AIA, CDT, LEED AP, PMP ARCHITECTS / ENGINEERS / INTERIOR 
DESIGNERS
7400 West Campus Rd.   Suite 150   New Albany, OH  43054   www.shremshock.com
t 614 545 4550 x 286     f 614 545 4555     [email protected]
Please consider the environment before printing this e-mail.


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Don Lowry
Sent: Tuesday, January 06, 2015 2:13 PM
To: [email protected]
Subject: RE: Foam & HangArs

Thanks for the info and apologies for the misspelling (hangArs).  This is not 
something I do on a regular basis. (I think I've only done 3 hangars since the 
80's).  

This reminds me of my first, Dyess Air Force base in Abilene, TX  back in the 
80s sometime when the B1 Bomber first came out, we did a hanger for it.  Very 
souped up foam systems(deluge), lots of monitors etc.  Impressive during the 
tests, system refilled & left in service.  About a month later we get a call 
that says they need more foam and their systems re-set up.  Seems a private on 
guard duty had "accidently" pulled the manual trip switch....The B1B in the 
hanger was opened up and needless to say had a lot of soap suds on the 
electronics.  Talk about a mess ☺. 

If I recall at that time the pop-up type sprinklers were not available and 
maybe were invented because of this!!  Good times back then.

Anyway thanks to all for the help.
Don Lowry, CET, Texas RME


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Bob Holland
Sent: Tuesday, January 06, 2015 12:28 PM
To: [email protected]
Subject: RE: Foam & HangArs

A few years ago while at URS I was part of a team doing hangars for Executive 
Jet, Nationwide, US Air, Tenn. Nat'l Guard, Proctor and Gamble and others, a 
bunch of them.  When we started NFPA 409 was only mentioned in a list of 
related applicable codes.  IBC 412. 4 through .6  did not exist.  IBC 412.4.6 
now lists what cannot happen in a hangar without foam.  I strongly advised 
getting a copy of IBC 412 with the Commentary. It is based on 409 but affords 
greater general clarity via the Commentary. Details remain in 409.
  
I've not seen a mention of draft curtains in the dialogue below.  As I recall 
these establish zones based upon allowable fire areas per construction type and 
a 75' circle 'sets off' the zones. Worst case is an interior zone (not left or 
right perimeter) where the 75' causes three zones to activate.  Water 
calculations were based on this.

There were several ways to deliver foam, overhead gets into aircraft and 
cannons can be obstructed or otherwise problematic.   The preferred method 
after it was developed with the air force was the
'pop-up' sprinklers in the drainage trench.  It took a couple of years to 
garner approval.  Sneaky aircraft prefer this method.  This system covers the 
floor where most fuel fires originate and drains away quickly if the floor is 
properly sloped and creates less mess.  A lot less.

There was a video in circulation many years ago of an overly concentrated AFFF 
- water mix filling a hangar.  Ellsworth AFB as I recall.  Its real.

For the more advanced and fool proof systems IR/FR detectors were used and 
abort buttons were located in numerous places.

Be aware of the pump redundancy requirement.

Effluent may be an issue.  We drained foam areas only through a weir with 
automatic sluice gates, normally open to storm through an OWS, when activated 
the OWS was by passed and the mess went to a rubber lined pond or a lined 
concrete tank for containment and gradual release to the sanitary sewer 
subsequent to communication with the local sewer district.  AFFF kills good 
bugs in a treatment plant.  

At one point sharing the effluent pond came up and with the help of actuaries 
determining the likelihood of two hangars on the same airfield in the same 72 
hour period was one to the negative eleventh.

Testing involves a dump unless otherwise accepted without it by the AHJ.  
Usually they've not seen such an event so plan on it.  If its overhead, cover 
the walls with plastic well secured.

ROBERT HOLLAND Jr. AIA, CDT, LEED AP, PMP ARCHITECTS / ENGINEERS / INTERIOR 
DESIGNERS
7400 West Campus Rd.   Suite 150   New Albany, OH  43054   www.shremshock.com
t 614 545 4550 x 286     f 614 545 4555     [email protected]
Please consider the environment before printing this e-mail.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Don Lowry
Sent: Tuesday, January 06, 2015 10:57 AM
To: [email protected]
Subject: RE: Foam & Hangers

Chris,
I believe this has already been hashed out with the owner / city but I have 
pointed out the IBC quote in case they missed it and will await a response, 
before I move forward in the design/pricing.
Thanks for all your help.

Don

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Cahill, Christopher
Sent: Tuesday, January 06, 2015 9:23 AM
To: [email protected]
Subject: RE: Foam & Hangers

If you meet the letter of the code the City doesn't get a vote. AHJ don't have 
to approve exception unless there is something to the effect of 
'exception...where approved by the building official....'.  In this case the 
exception doesn't say where approved. 

Are you storing only transient aircraft in a group II hangar?  Are there 
separate repair facilities? If that is the case you don't need foam no matter 
what the AHJ wants.  Now if you are storing aircraft based there (not
transient) for example you don't get the exception and the power position 
shifts to the AHJ.  There really aren't a lot of these kinds of hangars so you 
probably don't get the exception.  I was just offering another way out.


I've had a couple cities favorably rule based aircraft and light maintenance 
still met the exception thus no foam. But that creative interpretation of
the meaning and intent is up to the AHJ.    

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Don Lowry
Sent: Tuesday, January 06, 2015 8:51 AM
To: [email protected]
Subject: RE: Foam & Hangers

Thanks to all for the response, I was just verifying I was reading that 
correctly about the entire hanger being calced at once.

Chris,
Thanks for that reference, I will point that out to the project.  Awhile back 
the builder told me they had found an exception in the IBC where it didn't need 
foam but the city was not accepting that exception.  I will ask if this is the 
case?

Thanks,
Don Lowry

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Cahill, Christopher
Sent: Monday, January 05, 2015 5:43 PM
To: [email protected]
Subject: RE: Foam & Hangers

Seems to me it reads all 16,900 sq.ft. which is not typical with multiple 
systems in our world.  But do you even need foam?  See IBC:

[F] 412.4.6 Fire suppression.
Aircraft hangars shall be provided with a fire suppression system designed in 
accordance with NFPA 409, based upon the classification for the hangar given in 
Table 412.4.6.

Exception: Where a fixed base operator has separate repair facilities on site, 
Group II hangars operated by a fixed base operator used for storage of 
transient aircraft only shall have a fire suppression system, but the system is 
exempt from foam requirements.

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns & McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Don Lowry
Sent: Monday, January 05, 2015 4:06 PM
To: [email protected]
Subject: Foam & Hangers

Ref 2004 NFPA-409

 

Situation:

Group II hanger

Option # 4, Closed-Head Foam-Water Sprinkler System 

 

16,900 Sq Ft total hanger size

 

So, per 7.6.4 we'll need 2 systems (8K and 8900) respectively so as not to 
exceed 15k per system.

 

7.6.2 states minimum design density .16 gpm/sqft over entire storage and 
service area.

 

Question; 

Based on 7.6.2  I've got to calc both systems at the same time, for the
entire hanger area. (lots of water).   Am I interpreting this correctly or
does this mean calc the entire area of each systems individual floor area?

 

Thanks in advance,

 

Don Lowry

 

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to