Equivalent options for CARTONED so I’m assuming the one with face sprinklers is 
not high on the preferred list.  For uncartoned non-expanded you have to use 
the one that specifically states that (which was the preferred one anyways I 
imagine).


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Jan 13, 2015, at 1:42 PM, Dewayne Martinez 
> <[email protected]> wrote:
> 
> NFPA 13 (07ed) Section 17.3.4.1
> 
> I have rack storage of plastic over 25ft high without solid shelves, double
> row racks,8ft wide aisles.
> 
> It seems to comply with both  17.3.4.1.1 and 17.3.4.1.4, do I just pick
> which one works out best for me?
> 
> Thanks,
> 
> Dewayne