David,
could you check your section references? I couldn't find anything
in the '13 edition after 17.3.3.4.7, and there wasn't any reference
ending in ".1.1" after 17.3.1.1. I did see that 17.3.1.1 notes that the
protection methods described in section 17.3.1 for CMDA sprinklers are
only applicable when the plastics - either expanded or unexpanded - are
in cartons. Similar notes are found in 17.3.1.4, and 17.3.1.5.
Am I reading your references correctly?
*
PARSLEY CONSULTING
*
Ken Wagoner
760.745.6181 voice
760.745.0537 fax
website:
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>
On 1/18/2015 2:22 PM, David Bitton wrote:
The requirements of 17.3.4.1.1 are considerably more demanding than those
outlined in 17.3.4.1.4. I cannot envision a situation where the former
would be a more economical solution. The main difference that I can see is
that 17.3.4.1.1 applies to "Group A Plastic Commodities" whereas Fig.
17.3.4.1.4 can only be used for "Cartoned Expanded and Unexpanded Plastic
and Uncartoned Unexpanded Plastic". This means that if you have Uncartoned
Expanded Plastic, you have to use 17.3.4.1.1.
I wish that this section was written more clearly.
David
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of James Crawford
Sent: Friday, January 16, 2015 7:02 PM
To: [email protected]
Subject: RE: Rack storage question
I have always been under the assumption that it was up to the designer to
pick the option that worked the best, as available water pressure, owner
requirements and racking design would all play on which option to choose.
Some work better than others.
Just my opinion
Thank you
James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email [email protected]
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Dewayne Martinez
Sent: Wednesday, January 14, 2015 9:05 AM
To: SprinklerFORUM
Subject: FW: Rack storage question
Any takers on this one?
*From:* Dewayne Martinez [mailto:[email protected]]
*Sent:* Tuesday, January 13, 2015 3:43 PM
*To:* '[email protected]'
*Subject:* Rack storage question
NFPA 13 (07ed) Section 17.3.4.1
I have rack storage of plastic over 25ft high without solid shelves, double
row racks,8ft wide aisles.
It seems to comply with both 17.3.4.1.1 and 17.3.4.1.4, do I just pick
which one works out best for me?
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org