Ken, The original question posed by Dewayne specifically mentioned the 2007 Edition. The 2010 Edition has the same references but this section underwent major changes for the 2013 Edition. Accordingly, Article 17.3.4.1.1 is now 17.3.1.5 and Fig. 17.3.4.1.4 is now Fig. 17.3.1.7. Article 17.3.1.5 of the 2013 Edition allows the designer to use any of the 3 in-rack protection schemes (17.3.1.5(a), 17.3.1.5 (b), or 17.3.1.7).
David -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Parsley Consulting Sent: Monday, January 19, 2015 9:43 AM To: [email protected] Subject: Re: Rack storage question David, could you check your section references? I couldn't find anything in the '13 edition after 17.3.3.4.7, and there wasn't any reference ending in ".1.1" after 17.3.1.1. I did see that 17.3.1.1 notes that the protection methods described in section 17.3.1 for CMDA sprinklers are only applicable when the plastics - either expanded or unexpanded - are in cartons. Similar notes are found in 17.3.1.4, and 17.3.1.5. Am I reading your references correctly? * PARSLEY CONSULTING * Ken Wagoner 760.745.6181 voice 760.745.0537 fax website: www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> On 1/18/2015 2:22 PM, David Bitton wrote: > The requirements of 17.3.4.1.1 are considerably more demanding than those > outlined in 17.3.4.1.4. I cannot envision a situation where the former > would be a more economical solution. The main difference that I can see is > that 17.3.4.1.1 applies to "Group A Plastic Commodities" whereas Fig. > 17.3.4.1.4 can only be used for "Cartoned Expanded and Unexpanded Plastic > and Uncartoned Unexpanded Plastic". This means that if you have Uncartoned > Expanded Plastic, you have to use 17.3.4.1.1. > > I wish that this section was written more clearly. > > David > -----Original Message----- > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of James Crawford > Sent: Friday, January 16, 2015 7:02 PM > To: [email protected] > Subject: RE: Rack storage question > > I have always been under the assumption that it was up to the designer to > pick the option that worked the best, as available water pressure, owner > requirements and racking design would all play on which option to choose. > Some work better than others. > > Just my opinion > > > > Thank you > > > James Crawford > Phaser Fire Protection Ltd. > Phone 604-888-0318 > Fax 604-888-4732 > Cel 604-790-0938 > Email [email protected] > > > > -----Original Message----- > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Dewayne Martinez > Sent: Wednesday, January 14, 2015 9:05 AM > To: SprinklerFORUM > Subject: FW: Rack storage question > > Any takers on this one? > > > > *From:* Dewayne Martinez [mailto:[email protected]] > *Sent:* Tuesday, January 13, 2015 3:43 PM > *To:* '[email protected]' > *Subject:* Rack storage question > > > > NFPA 13 (07ed) Section 17.3.4.1 > > I have rack storage of plastic over 25ft high without solid shelves, double > row racks,8ft wide aisles. > > It seems to comply with both 17.3.4.1.1 and 17.3.4.1.4, do I just pick > which one works out best for me? > > Thanks, > > Dewayne > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org