Doug,

You should only use factory pre mixed solutions.
It has been this way for years.

Forest Wilson
Fire Sprinkler Contractor
PH: 937-516-8248
[email protected]


-----Original Message-----
From: Douglas Hicks <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Fri, Jan 16, 2015 07:28 PM
Subject: Antifreeze, not enough



<div id="AOLMsgPart_1_e341065c-cf67-4969-8aa8-79f27d2e77d3" style="margin: 
0px;font-family: Tahoma, Verdana, Arial, Sans-Serif;font-size: 12px;color: 
#000;background-color: #fff;">

<pre style="font-size: 9pt;"><tt>We was called to install an isolation valve in 
a wet system, and replace the antifreeze. Another company made the wet system 
into an antifreeze system.  No signage, indicating the system was not a wet 
system but was an antifreeze system.   I was told the system held about 50 to 
55 gallons of glycol.  I ordered 12 of the 38% 5 gallon pre-mixed buckets, 60 
gallons.  I also had some straight glycol, that we mixed, for a total of 80 
gallons .    We got to the job site and drained the system, getting about 75 
gallons of fluid. The old antifreeze was dirty, but no lumps, no scale.   After 
installing the isolation valve, and test ports at each end of the system, we 
flushed and drained the system. We filled the system with fresh water and held 
the pressure for 10 minutes and had no visible leaks. Again we drained the 
system, using the vacuum to make sure we got all the old fluid out. We put in 
80 gallons, of pre-mix.  Our pressure reading was about 5 
 PSI.  I went into the highest att
 ic, loosened 2 heads and we had antifreeze leaking out.  At least it tasted 
like antifreeze, nasty tasting stuff. I tightened the heads and we went to the 
sprinkler room.  We added 12 gallons of straight water.  Still not enough 
pressure, so we opened the main control valve.  That is when I found out the 
50-60 gallon estimate came from the alarm guy, when he flowed water for his 
annual test.  So the maintenance guy & I went to his office and finally found 
some information that noted there was 110 gallons of water in the system.   So 
now I have a mix of antifreeze and straight water.   My thought is to drain 
15/20 gallons, then test the solution, and keep draining and testing until I 
get to 38% glycol.  Then we will add 38% until the system is full.  Or do we 
need to dump all the antifreeze and start over?  

We did have a problem filling the system with the pump.  Should we go to the 
highest accessible head and remove it, replacing it with a ball valve that we 
can open  and relieve the pressure?  Our pump has filled other systems without 
any problems.  

Douglas Hicks
General Fire Equipment Co of Eastern Oregon, Inc

_______________________________________________
Sprinklerforum mailing list
<a 
href="mailto:[email protected]";>[email protected]</a>
<a 
href="http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org";
 
target="_blank">http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org</a>
</tt></pre>
 <!-- end of AOLMsgPart_1_e341065c-cf67-4969-8aa8-79f27d2e77d3 -->
</div>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to