You would have to dump the antifreeze and start over.  You shouldn't be
using any solution other than a pre-mix and I don't think pre-mixing it
yourself counts.

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Douglas Hicks
Sent: Friday, January 16, 2015 11:33 AM
To: [email protected]
Subject: Antifreeze, not enough

We was called to install an isolation valve in a wet system, and replace the
antifreeze. Another company made the wet system into an antifreeze system.
No signage, indicating the system was not a wet system but was an antifreeze
system.   I was told the system held about 50 to 55 gallons of glycol.  I
ordered 12 of the 38% 5 gallon pre-mixed buckets, 60 gallons.  I also had
some straight glycol, that we mixed, for a total of 80 gallons .    We got
to the job site and drained the system, getting about 75 gallons of fluid.
The old antifreeze was dirty, but no lumps, no scale.   After installing the
isolation valve, and test ports at each end of the system, we flushed and
drained the system. We filled the system with fresh water and held the
pressure for 10 minutes and had no visible leaks. Again we drained the
system, using the vacuum to make sure we got all the old fluid out. We put
in 80 gallons, of pre-mix.  Our pressure reading was about 5 PSI.  I went
into the highest att
 ic, loosened 2 heads and we had antifreeze leaking out.  At least it tasted
like antifreeze, nasty tasting stuff. I tightened the heads and we went to
the sprinkler room.  We added 12 gallons of straight water.  Still not
enough pressure, so we opened the main control valve.  That is when I found
out the 50-60 gallon estimate came from the alarm guy, when he flowed water
for his annual test.  So the maintenance guy & I went to his office and
finally found some information that noted there was 110 gallons of water in
the system.   So now I have a mix of antifreeze and straight water.   My
thought is to drain 15/20 gallons, then test the solution, and keep draining
and testing until I get to 38% glycol.  Then we will add 38% until the
system is full.  Or do we need to dump all the antifreeze and start over?  

We did have a problem filling the system with the pump.  Should we go to the
highest accessible head and remove it, replacing it with a ball valve that
we can open  and relieve the pressure?  Our pump has filled other systems
without any problems.  

Douglas Hicks
General Fire Equipment Co of Eastern Oregon, Inc

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to