So the AHJ can simply write a policy and "BAM" it's legal to be more 
restrictive and costly? I always thought they had to submit to the building 
standards commission, no?

Sent from my iPhone

> On Jan 29, 2015, at 3:42 PM, Parsley Consulting <[email protected]> 
> wrote:
> 
> Adding to what Steve mentioned, it's also worth being very careful on which
> issues you care to fight over.   We've both run across AHJ's who  didn't 
> "follow
> the rules" on mandating local requirements, and the fight was more demanding
> than simply doing what was asked.
> 
> I emphasize that for me - not any reference to Steve - it cost me a client, 
> and any
> chance of ever getting a submittal through that AHJ in the future.  People are
> human.
> 
> *Ken Wagoner, SET
> *Parsley Consulting***
> *350 West 9th Avenue, Suite 206
> *Escondido, California 92025
> *****Phone 760-745-6181*
> Visit our website <http://www.parsleyconsulting.com/>
> 
> 
> ***
>> On 1/29/2015 3:37 PM, Steve Leyton wrote:
>> Depends on whether it's ordained, or a local code amendment or policy
>> bulletin or just an off-handed comment.   Local fire and building
>> officials have several different statutory methods that they can use to
>> make requirements that are more restrictive (or less) or beyond the
>> minimum prescriptives of a code or standard.  But in theory, it's
>> supposed to be substantiated, documented and published in the public
>> domain.   So as far as whether the AHJ you're referring to can make such
>> a requirement "...without an amendment ..." as you say, all depends on
>> what the local municipal code and/or city manager and/or city attorney
>> would say if you threw off the gloves.
>> 
>> My opinion only,
>> Steve Leyton
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:[email protected]] On Behalf Of
>> [email protected]
>> Sent: Thursday, January 29, 2015 3:29 PM
>> To: [email protected]
>> Subject: 13D exterior overhangs.
>> 
>> 13D does not require heads in exterior over-hangs, such as a second
>> story over-hanging a driveway. Can an AHJ apply 13 rules to 13D systems
>> without an amendment and require heads in over-hangs 4' & greater?
>> 
>> Sent from my iPhone
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
>> .org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to