Sean, this may not be so much a code issue but an equipment protection issue. The reasoning for the pre-action system is to protect what is in the room from a potential leak of water. I have always been required to use the dry pendent drops in these applications for this reason. Nothing to do with freezing. My opinion.
Lamar Vaughn, SET On Mon, Mar 16, 2015 at 10:03 PM, Sean Lockyer <[email protected]> wrote: > Even though (non-dry) pendent sprinklers must be installed on return bends > on dry systems what about pendent sprinklers in a heated/conditioned space > that is protected by a double-interlock, pre-action system (such as a video > production room, etc.) ? > > Does the fact that it is above a conditioned ceiling space matter ? To my > knowledge there is nothing in NFPA codes or the manufacturers listing that > give you an allowance for special situations like this but I was wondering > if anyone else has any experience with this sort of issue ? > > I would like to hear everybody's thoughts.. > > > Sean Lockyer > Project Designer 4617 > Parkbreeze Court > Cell 386-279-1197 Orlando, > Florida 32808 > [email protected] Phone: > 407-816-9101 > www.AITLifeSafety.com Fax: > 407-816-9104 > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org