Corrosion is a real possibility.  We have seen drops corroded shut on ferrous 
pipe due to water that was left within after testing (or a trip or whatever). A 
'rust plug' had formed across the entire cross section of the drop.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Tuesday, March 17, 2015 7:48 AM
To: [email protected]
Subject: RE: Pendent sprinklers on return bends on a pre-action system

You could also face corrosion issues if you have drops that are filled with 
water.