We have the 911 room for Boston Police at their headquarters and after
draining each and every return-bend head off their 2 preaction systems last
year, we installed a shut-off.
The client was very nervous about having ANY water in the drops, even under
30 PSI of air.  You have to trip these valves so everything will get wet
(inside).
Not a direct answer to the original post but even if I could, I wouldn't use
return bends where main frames, media, etc., are located.
TD

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Lamar Vaughn
Sent: Tuesday, March 17, 2015 8:42 AM
To: Sprinkler Forum
Subject: Re: Pendent sprinklers on return bends on a pre-action system

Sean, this may not be so much a code issue but an equipment protection
issue. The reasoning for the pre-action system is to protect what is in the
room from a potential leak of water. I have always been required to use the
dry pendent drops in these applications for this reason. Nothing to do with
freezing. My opinion.

Lamar Vaughn, SET

On Mon, Mar 16, 2015 at 10:03 PM, Sean Lockyer <[email protected]>
wrote:

> Even though (non-dry) pendent sprinklers must be installed on return 
> bends on dry systems what about pendent sprinklers in a 
> heated/conditioned space that is protected by a double-interlock, 
> pre-action system (such as a video production room, etc.) ?
>
> Does the fact that it is above a conditioned ceiling space matter ? To 
> my knowledge there is nothing in NFPA codes or the manufacturers 
> listing that give you an allowance for special situations like this 
> but I was wondering if anyone else has any experience with this sort of
issue ?
>
> I would like to hear everybody's thoughts..
>
>
>               Sean Lockyer
>               Project Designer                               4617
> Parkbreeze Court
>               Cell    386-279-1197                              Orlando,
> Florida 32808
>               [email protected]              Phone:
> 407-816-9101
>               www.AITLifeSafety.com                       Fax:
> 407-816-9104
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to