Correct, but NFPA 13 states to use a sidewall sprinkler and they are not allowed for Extra Hazard. Thus, one could assume the committee knew what is what doing and was stating an ordinary hazard design was acceptable. The Annex reference being quoted by the AHJ is not enforceable.
-----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Matthew J Willis Sent: Wednesday, April 01, 2015 10:21 AM To: [email protected] Subject: RE: Bottom of elevator shaft protection Especially when you through in, 8.15.5.2 The sprinkler required at the bottom of the elevator hoistway by 8.15.5.1 shall not be required for enclosed, noncombustible elevator shafts that do not contain combustible hydraulic fluids. So there is the correlation for "combustible hydraulic fluids" R/ Matt Matthew J. Willis Project Manager Rapid Fire Protection Inc. 1805 Samco Road Rapid City, SD 57702 Office-605.348.2342 Cell-605.391.2733 Fax:-605.348.0108 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Matthew J Willis Sent: Wednesday, April 01, 2015 8:03 AM To: [email protected] Subject: RE: Bottom of elevator shaft protection Oh, trust me, I am all for it. However when the elevator is hydraulic, and the AHJ points to that very section, and then the big ram in the bottom..,which leg do we stand on? R/ Matt Matthew J. Willis Project Manager Rapid Fire Protection Inc. 1805 Samco Road Rapid City, SD 57702 Office-605.348.2342 Cell-605.391.2733 Fax:-605.348.0108 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of John Denhardt Sent: Wednesday, April 01, 2015 7:47 AM To: '[email protected]' Subject: RE: Bottom of elevator shaft protection There are several issues with this approach: - Sidewall sprinklers are only allowed for light or ordinary hazard and under overhead doors (NFPA 13 - 2013: 8.4.2). - NFPA 13 - 2013: 8.15.5.1 requires sidewall sprinklers for the bottom of the elevator pit. - NFPA 13 - 2013: A.8.15.5.1 "The sprinklers in the pit are intended to protect against fires caused by debris, which can accumulate over time. Ideally, the sprinklers should be located near the side of the pit below the elevator doors, where most debris accumulates. However, care should be taken that the sprinkler location does not interfere with the elevator toe guard, which extends below the face of the door opening." No mention of combustible hydraulic fluid. Extra Hazard??????? Just thinking out loud! John -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Matthew J Willis Sent: Wednesday, April 01, 2015 9:36 AM To: [email protected] Subject: RE: Bottom of elevator shaft protection I had the 10 in parenthesis, my apologies Also I forgot to add.., OH1 because it is a mechanical room after all. R/ Matt Matthew J. Willis Project Manager Rapid Fire Protection Inc. 1805 Samco Road Rapid City, SD 57702 Office-605.348.2342 Cell-605.391.2733 Fax:-605.348.0108 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of John Denhardt Sent: Wednesday, April 01, 2015 7:28 AM To: '[email protected]' Subject: RE: Bottom of elevator shaft protection What year is your reference? NFPA 13 - 2013? John -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Matthew J Willis Sent: Wednesday, April 01, 2015 9:01 AM To: [email protected] Subject: RE: Bottom of elevator shaft protection Ordinary if not hydraulic. EHI if combustible hydraulic fluid is used. A.5.4.1 (10) R/ Matt Matthew J. Willis Project Manager Rapid Fire Protection Inc. 1805 Samco Road Rapid City, SD 57702 Office-605.348.2342 Cell-605.391.2733 Fax:-605.348.0108 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Mike Hairfield Sent: Wednesday, April 01, 2015 5:35 AM To: [email protected] Subject: RE: Bottom of elevator shaft protection Some AHJ's classify it as Extra Hazard because of the Hydraulic Fluid, I wouldsay ordinary hazard but never light hazard. Mike > From: [email protected] > To: [email protected] > Subject: Bottom of elevator shaft protection > Date: Wed, 1 Apr 2015 11:31:30 +0000 > > Question, > Would the bottom of the elevator shaft be considered light or ordinary hazard > ? We have an elevator shaft 15-'4" wide, one head would be acceptable as > light hazard but not as ordinary hazard. > > > Stephen J. Sorrell, CET > NICET# 77901 Level III > E mail: > [email protected]<mailto:[email protected]> > > Performance Fire Protection, LLC > Corporate Office > 179 Gasoline Alley - PO Box 4510 > Mooresville, NC 28117 > Phone: 704-663-1664 Fax: 704-663-1652 Cell : 704-309-1242 > > Web: www.performancefire.com<http://www.performancefire.com> > Licensed in NC, SC, VA, TN, GA, AL > > "Performance on Every Level." > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org