Read the text from the NFPA 13 handbook:
"Refuse and residual hydraulic fluids tend to collect at the bottom of shafts. 
A properly located sprinkler, as required by 8.15.5.1, can control a fire of 
such material. Conventional requirements regarding the placement of the 
deflector and clear space below the sprinkler cannot always be adhered to in 
this area. These issues are not critical, however, because the sprinkler would 
be physically close to any point where a fire could originate, still allowing 
the sprinkler to control the fire."

IMHO, it seems you are applying room design methods to an elevator shaft which 
I don't believe is the intent of the code.  One approach is to follow the 
sprinkler head listings for coverage area and provide enough to cover the 
entire space.

 Brett Foreman, PE


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Sorrell
Sent: Wednesday, April 01, 2015 7:32 AM
To: [email protected]
Subject: Bottom of elevator shaft protection

Question,
Would the bottom of the elevator shaft be considered light or ordinary hazard ? 
We have an elevator shaft 15-'4" wide, one head would be acceptable as light 
hazard but not as ordinary hazard.


Stephen J. Sorrell, CET
NICET# 77901 Level III
E mail: [email protected]<mailto:[email protected]>

Performance Fire Protection, LLC
Corporate Office
179 Gasoline Alley -  PO Box 4510
Mooresville, NC 28117
Phone: 704-663-1664  Fax: 704-663-1652
Cell : 704-309-1242

Web: www.performancefire.com<http://www.performancefire.com>
Licensed in NC, SC, VA, TN, GA, AL

"Performance on Every Level."

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to