Don't wrap it on the in rack piping. We had a warehouse freezer where a fork lift driver took out the sprinkler pipe and broke the Protectowire. I don't need to tell you what a mess it was
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 www.fpdc.com > On Apr 15, 2015, at 10:38 AM, Brian Harris <[email protected]> wrote: > > Working on a 30,000 sq.ft freezer with a pre-action system for the ceiling > and a pre-action system for the racks, was curious to see what is the > preferred way to add the detection. If you use protectowire will it even trip > if you install it on the rack piping since there is nothing to collect the > heat? Do you only wrap the pipe at the ceiling? Etc? > > Brian Harris, CET > BVS Systems Inc. > Sprinkler Division > bvssystemsinc.com<http://bvssystemsinc.com/> > Phone: 704.896.9989 > Fax: 704.896.1935 > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org