I agree Steve and I am breathing a sigh of relief because I know I have not 
included standpipes for buildings that have mezzanines above 30' but where the 
highest story is below 30'.

So, what's up with that Figure 905.3.1(1) in the 2012 IFC?  Am I looking at 
that wrong or should that be fixed?

Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Wednesday, April 22, 2015 11:35 AM
To: [email protected]
Subject: RE: Standpipes

Don't get lost/confused in that.   Let's say it's occupied - it's not a
floor.  Period.

Now, if the BO or FO wants to make a ruling or interpretation that it is, or 
that they want standpipes, that's a different issue.  But it's
not a floor and should not could toward or past 30'-0".   A mezzanine is
not accessed through a protected stair and a mezzanine fire can be
fought from within the unit.

Steve





-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Matthew J 
Willis
Sent: Wednesday, April 22, 2015 9:17 AM
To: [email protected]
Subject: RE: Standpipes

Sounds like an attic, not a loft.
It will not be occupied right?


R/
Matt


Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.
1805 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Cell-605.391.2733
Fax:-605.348.0108



-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of David Autry
Sent: Wednesday, April 22, 2015 10:09 AM
To: [email protected]
Subject: RE: Standpipes

Travis,
I can't quote code. We had the same thing and the City required Standpipes.

David Autry

Meininger Fire Protection
2521 West L Street, Suite 5
Lincoln, NE 68522
402.466.2616
402.466.2617 fax
[email protected]


-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Travis Mack
Sent: Wednesday, April 22, 2015 10:38 AM
To: <[email protected]>
Subject: Standpipes

Does a loft/mezzanine count toward the height to require a standpipe?

Example: 4th floor is 29'-4" above lowest level of fire department access.
So standpipe would not be required.

But these units have a loft/mezzanine that will be obviously above the 30'. The 
only way to access the loft is from a stair in the unit on the fourth floor.

So standpipes yes or no? It is an R-2 occupancy.

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to