2012 IFC, 905.3.1 Height. Class III standpipe systems shall be installed throughout buildings where the floor level of the highest story is located more than 30 feet above the lowest level of the FD vehicle access...
There is nothing about the "story" being occupied or not so I believe you have to count the mezzanine. Actually, Figure 905.3.1(1) in the IFC shows a section with the dimension line drawn to a floor labeled "Mezzanine" and a note that says "Highest Floor Level of Highest Story". The commentary states this also, "The threshold based on the height of the building is independent of the occupancy of the building, the area of the building or the presence of an automatic sprinkler system. This is based on the universal need to be able to provide a water supply for fire suppression in any building and on the limitations of the physical effort necessary to extend hose lines vertically." Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | http://www.kfiengineers.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack Sent: Wednesday, April 22, 2015 10:38 AM To: <[email protected]> Subject: Standpipes Does a loft/mezzanine count toward the height to require a standpipe? Example: 4th floor is 29'-4" above lowest level of fire department access. So standpipe would not be required. But these units have a loft/mezzanine that will be obviously above the 30'. The only way to access the loft is from a stair in the unit on the fourth floor. So standpipes yes or no? It is an R-2 occupancy. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org