Don't pin this on ME!!!

But I do disagree with the figure - it contradicts the letter of the
code.

#gettingsuckedintothevortex





-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
rongreenman .
Sent: Wednesday, April 22, 2015 10:08 AM
To: [email protected]
Subject: Re: Standpipes

So this is what I get for believing the illustrations are explanations
of text. Woe under us visual learners.

On Wed, Apr 22, 2015 at 10:01 AM, Reed A. Roisum, SET
<[email protected]>
wrote:

> Steve agrees that the IFC commentary figure does not agree with the 
> code language and should be disregarded.  A mezzanine is clearly not a
story.
> Sorry for the confusion...I thought I was safe when I was just quoting

> what I read in the code commentary.
>
> Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire 
> Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile: 
> 701.388.1352 | http://www.kfiengineers.com
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Steve 
> Leyton
> Sent: Wednesday, April 22, 2015 11:45 AM
> To: [email protected]
> Subject: RE: Standpipes
>
> Reed:
>
> We use CA amended IFC 2012: Section 905.3.1 has been amended and the
> figure does not appear in my CA code.   Email it to me off-forum
please.
>
> SL
>
>
>
>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of 
> Reed A. Roisum, SET
> Sent: Wednesday, April 22, 2015 9:41 AM
> To: [email protected]
> Subject: RE: Standpipes
>
> I agree Steve and I am breathing a sigh of relief because I know I 
> have not included standpipes for buildings that have mezzanines above 
> 30' but where the highest story is below 30'.
>
> So, what's up with that Figure 905.3.1(1) in the 2012 IFC?  Am I 
> looking at that wrong or should that be fixed?
>
> Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire 
> Protection Designer | Fargo, ND | direct: 701.552.9903 | mobile:
> 701.388.1352 | http://www.kfiengineers.com
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of 
> Steve Leyton
> Sent: Wednesday, April 22, 2015 11:35 AM
> To: [email protected]
> Subject: RE: Standpipes
>
> Don't get lost/confused in that.   Let's say it's occupied - it's not
a
> floor.  Period.
>
> Now, if the BO or FO wants to make a ruling or interpretation that it 
> is, or that they want standpipes, that's a different issue.  But it's
> not a floor and should not could toward or past 30'-0".   A mezzanine
is
> not accessed through a protected stair and a mezzanine fire can be 
> fought from within the unit.
>
> Steve
>
>
>
>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of 
> Matthew J Willis
> Sent: Wednesday, April 22, 2015 9:17 AM
> To: [email protected]
> Subject: RE: Standpipes
>
> Sounds like an attic, not a loft.
> It will not be occupied right?
>
>
> R/
> Matt
>
>
> Matthew J. Willis
> Project Manager
> Rapid Fire Protection Inc.
> 1805 Samco Road
> Rapid City, SD 57702
> Office-605.348.2342
> Cell-605.391.2733
> Fax:-605.348.0108
>
>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of 
> David Autry
> Sent: Wednesday, April 22, 2015 10:09 AM
> To: [email protected]
> Subject: RE: Standpipes
>
> Travis,
> I can't quote code. We had the same thing and the City required
Standpipes.
>
> David Autry
>
> Meininger Fire Protection
> 2521 West L Street, Suite 5
> Lincoln, NE 68522
> 402.466.2616
> 402.466.2617 fax
> [email protected]
>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of 
> Travis Mack
> Sent: Wednesday, April 22, 2015 10:38 AM
> To: <[email protected]>
> Subject: Standpipes
>
> Does a loft/mezzanine count toward the height to require a standpipe?
>
> Example: 4th floor is 29'-4" above lowest level of fire department
access.
> So standpipe would not be required.
>
> But these units have a loft/mezzanine that will be obviously above the

> 30'. The only way to access the loft is from a stair in the unit on 
> the fourth floor.
>
> So standpipes yes or no? It is an R-2 occupancy.
>
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook:
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>
> Sent from my iPhone
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .o
> rg
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud
service.
> For more information please visit http://www.symanteccloud.com 
> ______________________________________________________________________
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud
service.
> For more information please visit http://www.symanteccloud.com 
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud
service.
> For more information please visit http://www.symanteccloud.com 
> ______________________________________________________________________
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud
service.
> For more information please visit http://www.symanteccloud.com 
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to