Thanks Roland, but instead of additional complexity I would call it logical
consistency, along the lines of:

"Where Minimum Operating Pressure is used in this standard, it shall mean
the calculated normal pressure, Pn, at the sprinkler".

just a suggestion that might appeal to the "Calculation Procedures purists"
in a lot of us!!!

Brad

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Roland Huggins
Sent: Friday, April 24, 2015 11:00 AM
To: [email protected]
Subject: Re: Suggestion for new definition in NFPA #13- Operating Pressure.

Since other than NFPA 15 systems, virtually NO ONE applies Pv so why add the
additional complexity.  This is especially true with Pt being a MORE
conservative approach.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Apr 24, 2015, at 8:11 AM, Brad Casterline <[email protected]>
wrote:
> 
> Working pressure is defined, and used in a few places in the text.
Operating
> Pressure is not defined but is used extensively and is obviously meant to
be
> used to calculate the discharge rate of sprinkler heads. According to
> Webster's, Working and Operating are synonymous, but this results in a
> problem where ~minimum operating pressure (for sprinklers) shall be 7
psi~,
> due to the "2nd head phenomena", where the Pv between the end and 2nd
heads
> exceeds the Pf, making Pn at the 2nd head less than 7 psi. Since only the
Pn
> produces flow at the 2nd head we are "allowed" to subtract Pv.
> 
> 
> 
> So the suggestion for the definition of Operating Pressure regarding
> sprinkler discharge is to specify minimum Pn shall be 7 psi.
> 
> 
> 
> Just wanted to get that off my chest.
> 
> 
> 
> thanks,
> 
> 
> 
> 
> 
> Brad Casterline, NICET IV
> 
> Fire Protection Division
> 
> 
> 
> FSC, Inc.
> 
> P: 913-722-3473
> 
> [email protected]
> 
> www.fsc-inc.com
> 
> 
> 
> Engineering Solutions for the Built Environment
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to