Normally I would send this email directly to you but I wanted to correct something to the group. I do ask IF this thread continues that we take it off the Forum and send it directly to the interested party.
That correction is to KILL KILL KILL any reference to a velocity limit AND the erroneous assumption that D-W is more accurate for sprinkler calculations with assigned higher velocities or any calculation for that matter using water. VELOCITY DOES NOT IMPACT THE VALIDITY OF THE H-W EQUATION. H-W is needed for antifreeze due to the viscosity issue. I would discourage anyone from using D-W or the Pt method based solely on better communication with the AHJ. You don’t get a better system, just unnecessary complications. Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Apr 26, 2015, at 9:00 AM, Brad Casterline <[email protected]> wrote: > > Dear Roland and Cecil, > > I appreciate what you both said. I guess what made me gun shy is how you > inferred so much from: > > 1) my subject line, > 2) my reasoning in the original post for the subject line, and, > 3) my suggested definition in my 2nd post. > > This is not about fluid mechanics. It is about what NFPA #13 has to say > about the application of fluid mechanics to sprinkler systems. It is in this > latter context where "logical consistency" should apply. > > It is beside the point, but I have used Pt to calculate Q in 99.9% of the > many hundreds of calcs I have done in the last 40 years (next month). For > the first 20 I really had no frigging idea exactly was I was doing. I just > knew if I adhered strictly to the rules it would be OK. Then I discovered > "The Law of Falling Bodies" and soon sprinkler calcs made sense. > > I know you big shot T.C. members "giveth and you taketh away". If I only got > one wish for a change in calculation procedure, it would be to use > Darcy-Weisbach instead of Hazen-Williams. (62.4 lbs/ft^3, 1.01 centipoises). > For 'Performance' based calculations there is nothing sweeter, in my view, > than using D-W AND subtracting the velocity component of the pressure where > it is not acting normal. > > Cecil, are you aware that H-W is conservative over D-W, until you get to > about 20 ft/sec (for C=120)? So for Elegance you should push to either limit > the velocity to 20 ft/sec or make us use D-W. To limit the velocity AND use > H-W would be like killing flies with a sledge hammer... not very elegant, > eh? > > thanks, > Brad Casterline > AFSA Designer Member* and SET > > *couple months behind on this years dues but i promise come next payday i'll > put the check in the mail _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org