Normally I would send this email directly to you but I wanted to correct 
something to the group.  I do ask IF this thread continues that we take it off 
the Forum and send it directly to the interested party.

That correction is to KILL KILL KILL any reference to a velocity limit AND the 
erroneous assumption that D-W is more accurate for sprinkler calculations with 
assigned higher velocities or any calculation for that matter using water. 
VELOCITY DOES NOT IMPACT THE VALIDITY OF THE H-W EQUATION. H-W is needed for 
antifreeze due to the viscosity issue.  

I would discourage anyone from using D-W or the Pt method based solely on 
better communication with the AHJ.  You don’t get a better system, just 
unnecessary complications.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Apr 26, 2015, at 9:00 AM, Brad Casterline <[email protected]> wrote:
> 
> Dear Roland and Cecil,
> 
> I appreciate what you both said. I guess what made me gun shy is how you
> inferred so much from:
> 
> 1) my subject line,
> 2) my reasoning in the original post for the subject line, and,
> 3) my suggested definition in my 2nd post.
> 
> This is not about fluid mechanics. It is about what NFPA #13 has to say
> about the application of fluid mechanics to sprinkler systems. It is in this
> latter context where "logical consistency" should apply.
> 
> It is beside the point, but I have used Pt to calculate Q in 99.9% of the
> many hundreds of calcs I have done in the last 40 years (next month). For
> the first 20 I really had no frigging idea exactly was I was doing. I just
> knew if I adhered strictly to the rules it would be OK. Then I discovered
> "The Law of Falling Bodies" and soon sprinkler calcs made sense. 
> 
> I know you big shot T.C. members "giveth and you taketh away". If I only got
> one wish for a change in calculation procedure, it would be to use
> Darcy-Weisbach instead of Hazen-Williams. (62.4 lbs/ft^3, 1.01 centipoises).
> For 'Performance' based calculations there is nothing sweeter, in my view,
> than using D-W AND subtracting the velocity component of the pressure where
> it is not acting normal.
> 
> Cecil, are you aware that H-W is conservative over D-W, until you get to
> about 20 ft/sec (for C=120)? So for Elegance you should push to either limit
> the velocity to 20 ft/sec or make us use D-W. To limit the velocity AND use
> H-W would be like killing flies with a sledge hammer... not very elegant,
> eh?
> 
> thanks,
> Brad Casterline
> AFSA Designer Member* and SET
> 
> *couple months behind on this years dues but i promise come next payday i'll
> put the check in the mail

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to