Thanks Cecil.

I'd better hightail it out of here... i sense a T.C. member lynch party
forming... again...

b

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Sprinkler Academy - C Bilbo
Sent: Friday, April 24, 2015 11:49 AM
To: [email protected]
Subject: RE: Suggestion for new definition in NFPA #13- Operating Pressure.

So I'll jump in before Roland pops a vein......

Logical consistency would suggest that a simpler process that provided built
in safety and additional protection would be the process of choice.
 
Calculations using Pn are more complex and less conservative.  There is no
such thing as pure calculations regarding fire sprinkler systems.   One may
choose to apply as many variables as one wishes, but with fluctuating values
for those variables, there can be no pure calculation.  Therefore,
consistency requires our use of the simpler and more conservative approach.
I'd call it elegant.

It should be recognized that the above is my opinion as a member of the
NFPA, and has not been processed as a formal interpretation in accordance
with the NFPA Regulations Governing Committee Projects and should therefore
not be considered, nor relied upon, as the official position of the the
NFPA, nor any of their technical committees. 

Sincerely,


Cecil Bilbo 
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com

[email protected]

 

OUR STUDENTS SAVE LIVES!!


 
> From: [email protected]
> To: [email protected]
> Subject: RE: Suggestion for new definition in NFPA #13- Operating
Pressure.
> Date: Fri, 24 Apr 2015 11:16:54 -0500
> 
> Thanks Roland, but instead of additional complexity I would call it
logical
> consistency, along the lines of:
> 
> "Where Minimum Operating Pressure is used in this standard, it shall mean
> the calculated normal pressure, Pn, at the sprinkler".
> 
> just a suggestion that might appeal to the "Calculation Procedures
purists"
> in a lot of us!!!
> 
> Brad
> 
> -----Original Message-----
> From: Sprinklerforum
[mailto:[email protected]]
> On Behalf Of Roland Huggins
> Sent: Friday, April 24, 2015 11:00 AM
> To: [email protected]
> Subject: Re: Suggestion for new definition in NFPA #13- Operating
Pressure.
> 
> Since other than NFPA 15 systems, virtually NO ONE applies Pv so why add
the
> additional complexity.  This is especially true with Pt being a MORE
> conservative approach.
> 
> 
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org <http://www.firesprinkler.org/>
> 
> 
> 
> 
> 
> > On Apr 24, 2015, at 8:11 AM, Brad Casterline <[email protected]>
> wrote:
> > 
> > Working pressure is defined, and used in a few places in the text.
> Operating
> > Pressure is not defined but is used extensively and is obviously meant
to
> be
> > used to calculate the discharge rate of sprinkler heads. According to
> > Webster's, Working and Operating are synonymous, but this results in a
> > problem where ~minimum operating pressure (for sprinklers) shall be 7
> psi~,
> > due to the "2nd head phenomena", where the Pv between the end and 2nd
> heads
> > exceeds the Pf, making Pn at the 2nd head less than 7 psi. Since only
the
> Pn
> > produces flow at the 2nd head we are "allowed" to subtract Pv.
> > 
> > 
> > 
> > So the suggestion for the definition of Operating Pressure regarding
> > sprinkler discharge is to specify minimum Pn shall be 7 psi.
> > 
> > 
> > 
> > Just wanted to get that off my chest.
> > 
> > 
> > 
> > thanks,
> > 
> > 
> > 
> > 
> > 
> > Brad Casterline, NICET IV
> > 
> > Fire Protection Division
> > 
> > 
> > 
> > FSC, Inc.
> > 
> > P: 913-722-3473
> > 
> > [email protected]
> > 
> > www.fsc-inc.com
> > 
> > 
> > 
> > Engineering Solutions for the Built Environment
> > 
> > 
> > 
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to