We have a large manufacturing building, no interior walls,  we are looking
at and the owner has asked for OH2, then they have come back and requested
an area that they now wish to store 30' high with no in-rack protection.

 

Storage can be done with ESFR, the remainder of the building can be done
with QR brass uprights.

 

Question is do I require a draft curtain between the ESFR and the QR heads.
NFPA #13 (2013) 8.4.6.4 states the requirement for standard response heads, 

 

Just want to confirm.

 

 

Thank you

 

 