We have a large manufacturing building, no interior walls, we are looking at and the owner has asked for OH2, then they have come back and requested an area that they now wish to store 30' high with no in-rack protection.
Storage can be done with ESFR, the remainder of the building can be done with QR brass uprights. Question is do I require a draft curtain between the ESFR and the QR heads. NFPA #13 (2013) 8.4.6.4 states the requirement for standard response heads, Just want to confirm. Thank you James Crawford Phaser Fire Protection Ltd. Phone 604-888-0318 Fax 604-888-4732 Cel 604-790-0938 Email [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org