I would like to have them do the entire warehouse 430,000 ft2 but they only
have 20,000 ft2 of storage so probably won't happen



Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  [email protected]




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Roland Huggins
Sent: Friday, April 24, 2015 2:09 PM
To: [email protected]
Subject: Re: ESFR & QR heads

What Cecil said for NFPA 13. Their insurance carrier may whack you since
last time I checked (BEFORE THE BIG REVISION), FM required said separation
from all other sprinkler types and not just those with SR.

You can also do the whole building as ESFR so they can move their racks
around at their pleasure.  ESFR applies to LH and OH too.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Apr 24, 2015, at 1:51 PM, Sprinkler Academy - C Bilbo
<[email protected]> wrote:
> 
> It's all good.  No barrier required in your case.
> 
> It should be recognized that the above is my opinion as a member of the
NFPA, and has not been processed as a formal interpretation in accordance
with the NFPA Regulations Governing Committee Projects and should therefore
not be considered, nor relied upon, as the official position of the the
NFPA, nor any of their technical committees. 
> 
> Sincerely,
> 
> 
> Cecil Bilbo 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to