What Cecil said for NFPA 13. Their insurance carrier may whack you since last 
time I checked (BEFORE THE BIG REVISION), FM required said separation from all 
other sprinkler types and not just those with SR.

You can also do the whole building as ESFR so they can move their racks around 
at their pleasure.  ESFR applies to LH and OH too.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Apr 24, 2015, at 1:51 PM, Sprinkler Academy - C Bilbo 
> <[email protected]> wrote:
> 
> It's all good.  No barrier required in your case.
> 
> It should be recognized that the above is my opinion as a member of the NFPA, 
> and has not been processed as a formal interpretation in accordance with the 
> NFPA Regulations Governing Committee Projects and should therefore not be 
> considered, nor relied upon, as the official position of the the NFPA, nor 
> any of their technical committees. 
> 
> Sincerely,
> 
> 
> Cecil Bilbo 