Actually they were concerned that people would apply the shadow to obstructions 
such as ductwork vs. the 3 or 4 times rule.
At least that is how I remember it

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com






-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Roland Huggins
Sent: Thursday, April 23, 2015 3:29 PM
To: [email protected]
Subject: Re: Corridor shadow areas

the 13 committee rejected attempts to add a max shadowed area similar to 13R 
because it was too RESTRICTIVE.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Apr 23, 2015, at 10:59 AM, Ben Young <[email protected]> wrote:
> 
> Larry,
> 
> Thanks, I found it in the 2013 ROC, comment 13-143.  Its a shame, 
> because it sounds like they agreed but didn't like the backwall part 
> for some other reason.  McPhee's commentary in 13-135 would have made 
> the appendix language include areas behind sidewalls, but without 
> something like that, I have an AHJ basically telling me that this 
> scenario is only allowed in a 13R installation.  My indentations 
> aren't even as severe as those shown, they're only 12" deep by 5 feet 
> wide!  Oh well, I guess have something to submit next cycle now.
> 
> 
> Benjamin Young
> 
> On Thu, Apr 23, 2015 at 12:45 PM, Larry Keeping <[email protected]>
> wrote:
> 
>> The illustration that was first submitted for their consideration, 
>> was adjusted by the Technical Committee before it was accepted for 
>> addition into NFPA 13. The original submission showed a 9 ft wide by 
>> 2 ft deep entry vestibule on both sides of the corridor. I believe 
>> that when the figure was revised the "2 ft 0 in. max." should have been 
>> edited out.
>> 
>> Larry Keeping
>> 
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]] On Behalf Of Ben 
>> Young
>> Sent: April-23-15 12:01 PM
>> To: [email protected]
>> Subject: Corridor shadow areas
>> 
>> Does anyone know if there's an error with figure A.8.1.1(3)(a) in the 
>> 2013 edition of NFPA 13?
>> There appears to be an extraneous bit at the bottom that says '2 ft 0in.
>> max'
>> 
>> It looks like this is a holdover from a modification made to figure
>> 6.4.6.3.3.2 in the 2013 edition of NFPA 13R.
>> 
>> I'm wondering if the bottom of the figure accidentally got chopped 
>> off in the 13 version of the figure, and that the shadow areas behind 
>> the sidewalls in a hallway are allowed in a 13 system as well as a 13R 
>> system.
>> 
>> I checked the 2016 first and second draft reports but didn't see any 
>> comments or proposals regarding this, though.
>> 
>> Is this just wishful thinking on my part, or did someone goof up when 
>> they put the figure in?
>> 
>> Any thoughts?
>> 
>> Benjamin Young
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> ler.org
>> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to