Thank you very much

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jack Carlson
Sent: Thursday, April 30, 2015 8:51 AM
To: [email protected]
Subject: RE: help

NFPA 13 (2010 and 2013 Edition)

A.8.17.2 The fire department connection should be located not less than 18 in. 
(457 mm) and not more than 4 ft (1.2 m) above the level of the adjacent grade 
or access level.


Jack W. Carlson, SET
Triple "A" Fire Protection
Office - 251.649.2034
Fax - 251.649.2037
Cell - 706.247.5050

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of JONATHAN GARCIA
Sent: Thursday, April 30, 2015 10:43 AM
To: [email protected]
Subject: help

To whom it may concern

I am asking for the location in the code book NFPA or if it is in the IFC that 
indicates the height minimum and maximum for a FDC.

Thank you in advance

Jonathan Garcia
Fire Marshal/Investigator
1526 Stephanie Rd
Rio Rancho, NM 87124
Cell  (505) 238-7097
Office  (505) 891-5871
Fax  (505) 892-3178

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to