Unlike NFPA 13, NFPA 14 has the height requirement in the body and not the 
appendix.  From NFPA 14, 2007 edition:

6.4.6 Fire department connections shall be located not less than 18 in. (457 
mm) nor more than 48 in. (1219 mm) above the level of the adjoining ground, 
sidewalk, or grade surface.

Jack Fairchild

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of JONATHAN GARCIA
Sent: Thursday, April 30, 2015 11:07 AM
To: [email protected]
Subject: RE: help

Thank you very much

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Jack Carlson
Sent: Thursday, April 30, 2015 8:51 AM
To: [email protected]
Subject: RE: help

NFPA 13 (2010 and 2013 Edition)

A.8.17.2 The fire department connection should be located not less than 18 in. 
(457 mm) and not more than 4 ft (1.2 m) above the level of the adjacent grade 
or access level.


Jack W. Carlson, SET
Triple "A" Fire Protection
Office - 251.649.2034
Fax - 251.649.2037
Cell - 706.247.5050

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of JONATHAN GARCIA
Sent: Thursday, April 30, 2015 10:43 AM
To: [email protected]
Subject: help

To whom it may concern

I am asking for the location in the code book NFPA or if it is in the IFC that 
indicates the height minimum and maximum for a FDC.

Thank you in advance

Jonathan Garcia
Fire Marshal/Investigator
1526 Stephanie Rd
Rio Rancho, NM 87124
Cell  (505) 238-7097
Office  (505) 891-5871
Fax  (505) 892-3178

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to