Most Fire Codes allow the Chief to determine the location and criteria of the 
FDC.

 

Forest Wilson
Fire Sprinkler Contractor

[email protected]


 

 

-----Original Message-----
From: Fairchild, Jack <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Thu, Apr 30, 2015 11:52 am
Subject: RE: help


Unlike NFPA 13, NFPA 14 has the height requirement in the body and not the
appendix.  From NFPA 14, 2007 edition:

6.4.6 Fire department connections
shall be located not less than 18 in. (457 mm) nor more than 48 in. (1219 mm)
above the level of the adjoining ground, sidewalk, or grade surface.

Jack
Fairchild

-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of JONATHAN
GARCIA
Sent: Thursday, April 30, 2015 11:07 AM
To:
[email protected]
Subject: RE: help

Thank you very
much

-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Jack
Carlson
Sent: Thursday, April 30, 2015 8:51 AM
To:
[email protected]
Subject: RE: help

NFPA 13 (2010 and
2013 Edition)

A.8.17.2 The fire department connection should be located not
less than 18 in. (457 mm) and not more than 4 ft (1.2 m) above the level of the
adjacent grade or access level.


Jack W. Carlson, SET
Triple "A" Fire
Protection
Office - 251.649.2034
Fax - 251.649.2037
Cell -
706.247.5050

-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of JONATHAN
GARCIA
Sent: Thursday, April 30, 2015 10:43 AM
To:
[email protected]
Subject: help

To whom it may
concern

I am asking for the location in the code book NFPA or if it is in the
IFC that indicates the height minimum and maximum for a FDC.

Thank you in
advance

Jonathan Garcia
Fire Marshal/Investigator
1526 Stephanie Rd
Rio
Rancho, NM 87124
Cell  (505) 238-7097
Office  (505) 891-5871
Fax  (505)
892-3178

_______________________________________________
Sprinklerforum
mailing
list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum
mailing
list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum
mailing
list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum
mailing
list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to