8' stockpile of foam cups?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
860-608-4559 (cell)
Sent using CloudMagic [https://cloudmagic.com/k/d/mailapp?ct=ti&cv=6.0.64&pv=8.2]
On Wed, May 6, 2015 at 5:35 PM, [email protected]
<[email protected]> wrote:
It says, "... up to an 8' stockpile". So that would be from 1-86".





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On
Behalf Of [email protected]
Sent: Wednesday, May 06, 2015 2:34 PM
To: [email protected]
Subject: RE: Light & OH1 Hazard From Same Riser

8ft stockpile? What if the room is spread full of boxes of filters and other
junk and they're only 4ft high?

One pile 8ft high or 10 piles 4 ft high? One is LH and the other OH?

One is 100 sq. ft and the other 1,000 sq. ft.

This is going to be fun.

Craig L. Prahl
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC 29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension 74102
[email protected]

-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Tom Wellen
Sent: Wednesday, May 06, 2015 11:25 AM
To: [email protected]
Subject: Re: Light & OH1 Hazard From Same Riser

The next edition, 2016 will address mechanical rooms in the annex.

I submitted PI No. 514 to address mechanical rooms:

Public Input No. 514-NFPA 13-2013 [ Section No. A.5.3.1 ]
A.5.3.1
Ordinary hazard (Group 1) occupancies include occupancies having uses and
conditions similar to the following:
(1) Automobile parking and showrooms
(2) Bakeries
(3) Beverage manufacturing
(4) Canneries
(5) Dairy products manufacturing and processing
(6) Electronic plants
(7) Glass and glass products manufacturing
(8) Laundries
(9) Restaurant service areas
(10) Mechanical rooms with stockpiles up to 8 ft

Statement of Problem and Substantiation for Public Input A new mechanical room by definition is a light hazard occupancy. The room is empty and the equipment is generally noncombustible. The AHJ likely will not buy off that the room will
not be used for storage.

I also submitted Public Input No. 515-NFPA 13-2013 [ Section No. A.5.3.2 ] that
was rejected:
A.5.3.2
Ordinary hazard (Group 2) occupancies include occupancies having uses and
conditions similar to the following:
......
(31) Mechanical rooms with stockpiles up to 12 ft

Committee Statement
Resolution: The definition of OH2 will drive the user to this occupancy hazard
classification. This language is superfluous.


Tom Wellen


> On May 6, 2015, at 12:39 PM, Tim Stone <[email protected]> wrote:
>
> John,
> Answers to
> #1 YES.
> #2 NFPA 13 Chapter 5, current edition.
> #3 Of course you can, there is no restriction.
>
> Regards,
> G. Tim Stone
>
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician Fire Protection Sprinkler
> Design and Consulting Services
>
> 117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802) 434-4343
> [email protected]
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]]
> On Behalf Of John Allen, CET, CFPS
> Sent: Wednesday, May 06, 2015 1:27 PM
> To: [email protected]
> Subject: RE: Light & OH1 Hazard From Same Riser
>
> Okay, I'm really confused. In NFPA 13HB - 2013, I found the
following:
>
> FAQ: Can nonmetallic pipe be used in an ordinary hazard occupancy?
> Nonmetallic pipe is not permitted in ordinary hazard occupancies and
> is only permitted in specific small ordinary hazard rooms within light

> hazard occupancies. The limitation to rooms that do not exceed 400 ft2

> (37 m2) recognizes that almost all buildings have typically small
> storage rooms or mechanical rooms that would be categorized as
> ordinary hazard. Requiring a change in pipe type for those rooms or
> requiring the entire system to use metallic pipe would be
overburdensome.
>
> Supplement 3:
> (8)* Sprinklers shall not be required to be installed within
> electrical equipment, mechanical equipment, or air handling units not
> intended for occupancy.
> A.8.1.1(8) Equipment having access for routine maintenance should not
> be considered as intended for occupancy.
> Clarifies that some electrical equipment is large enough to be
> accessed by man doors. In these instances, where this equipment is not

> occupied but rather accessed for maintenance, sprinklers are not
required.
>
> So, my three questions now are:
> 1. do I need sprinklers in the mechanical room that is 750 sqf?
> 2. what code identifies the mechanical room as OH1?
> 3. if I do need sprinklers, can I design the OH1 area off the cross
> main that feeds the light hazard areas (using only one riser feed)?
>
>
> Best Regards,
>
> John Allen, CET, CFPS
> President
>
>
> AFS: Allen Fire & Security
> Your Safety is Our Success
> Direct: 770.715.7261 | Office: 770.723.7280 Ext 2 | Fax: 678.894.4180
>
>
> Please consider the environment before printing this email This
> email contains proprietary and confidential material for the sole use
> of the intended recipient and is the sole property of AFS. Any
> review, use, distribution or disclosure by others without the
> permission of the sender is strictly prohibited. If you are not the
> intended recipient (or authorized to receive for the recipient),
> please contact the sender by reply email and delete all copies of the
message.
>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]]
> On Behalf Of [email protected]
> Sent: Wednesday, May 6, 2015 8:56 AM
> To: [email protected]
> Subject: RE: Light & OH1 Hazard From Same Riser
>
> You are looking for permission? How long could the possible
scenarios in
> that list be?
>
> There is no restriction or prohibition of designing systems of
> different densities off one riser. It's common practice. Calculate
> and prove it works and you're done.
>
> Mechanical rooms contain rotating electrical equipment, some may
> contain natural gas or propane piping, or fuel oil, typically there's
> at least one or more boxes of filters since they go with the AC
> equipment, we will at some time probably have to consider the
> refrigerant being used on HVAC equipment as some of the "greener"
> gases have flammability properties. So HVAC mechanical rooms are not
> without hazards. OH 1 is typical for anything bigger than an
apartment closet mechanical room.
>
> Craig L. Prahl
> Fire Protection Group Lead
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC 29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension 74102
> [email protected]
>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]]
> On Behalf Of Brad Casterline
> Sent: Tuesday, May 05, 2015 6:14 PM
> To: [email protected]
> Subject: RE: Light & OH1 Hazard From Same Riser
>
> Apology accepted ;)
>
> a real head-scratcher--- i thought of a few things, looked them up,
> and by golly they were not codes that allows you to design that way
> (the way we all do all systems that is)
>
> i'm going home and let this bother me all night... thanks (i cant wait

> til tomorrow morning when i check my mail)
>
> brad
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]]
> On Behalf Of Jack Carlson
> Sent: Tuesday, May 05, 2015 4:51 PM
> To: [email protected]
> Subject: RE: Light & OH1 Hazard From Same Riser
>
> John,
>
> You should not have an issue with the design as described. Light and
> ordinary are commonly mixed, no separate supply main is necessary.
>
>
> Jack W. Carlson, SET
> Triple "A" Fire Protection
> Office - 251.649.2034
> Fax - 251.649.2037
> Cell - 706.247.5050
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]]
> On Behalf Of John Allen, CET, CFPS
> Sent: Tuesday, May 05, 2015 5:38 PM
> To: [email protected]
> Subject: Light & OH1 Hazard From Same Riser
>
> I apologize for such a simple question, but I would greatly appreciate

> some
> guidance:
>
> I have a 22,000 sqf light hazard office space with a 750 sqf
> mechanical room that I've identified as ordinary hazard 1. The entire

> ceiling space is an open 14' concrete beams and roof deck, and the
> mechanical room is separated by sheetrock and self-closing doors. The

> riser is in the mechanical room and I have 7 upright sprinkler heads
> fed off the cross main pipe feeding the light hazard office space.
> What code allows me to design this way or must I create a separate
riser feed for each hazard?
>
>
> Best Regards,
>
> John Allen, CET, CFPS
> President
>
>
> AFS: Allen Fire & Security
> Your Safety is Our Success
> Direct: 770.715.7261 | Office: 770.723.7280 Ext 2 | Fax: 678.894.4180
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to