I'll bring the rainbow wig and red nose for my facilitator.




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
rongreenman .
Sent: Thursday, May 07, 2015 11:49 AM
To: [email protected]
Subject: Re: Light & OH1 Hazard From Same Riser

Perhaps the better question is does the fire code allow storage in a
mechanical room. If no then it is the owners responsibility to insure
that this use is not allowed. I hate what if scenarios because a case of
styrofoam cups and a case of TP, and some filters and other
miscellaneous office supplies suddenly become cases of things. I got a
good deal on a truckload of styrofoam coffee cups so I sixteen pallets
of cups stacked to the ceiling in my mechanical room. I won't have to
buy cups again for a thousand years. Now where to put that railcar deal
I got on toilet paper?

And Steve. I was just too late in getting to this but I get to to
introduce you in Phoenix. I just got my lead in joke.


On Wed, May 6, 2015 at 7:53 PM, Cahill, Christopher
<[email protected]>
wrote:

> I hate to tell you but the below changes nothing.  I don't see where 
> mechanical rooms without stockpiles are addressed.  Mechanical rooms 
> with stockpiles by DESIGN are not all that common.  I'm not arguing in

> PRACTICE they are usually used for storage. FWIW I treat them as OHII 
> but in tight water situations when they are small or only have air 
> handlers then OHI would suffice.
>
> Chris Cahill, PE*
> Associate Fire Protection Engineer
> Burns & McDonnell
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
> *Registered in: MN
>
>
> Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work 
> For
>
> >
> >
> > -----Original Message-----
> > From: Sprinklerforum
> > [mailto:[email protected]] On Behalf Of

> > Tom Wellen
> > Sent: Wednesday, May 06, 2015 11:25 AM
> > To: [email protected]
> > Subject: Re: Light & OH1 Hazard From Same Riser
> >
> > The next edition, 2016 will address mechanical rooms in the annex.
> >
> > I submitted PI No. 514 to address mechanical rooms:
> >
> > Public Input No. 514-NFPA 13-2013 [ Section No. A.5.3.1 ]
> > A.5.3.1
> > Ordinary hazard (Group 1) occupancies include occupancies having 
> > uses
> and conditions similar to the following:
> > (1) Automobile parking and showrooms
> > (2) Bakeries
> > (3) Beverage manufacturing
> > (4) Canneries
> > (5) Dairy products manufacturing and processing
> > (6) Electronic plants
> > (7) Glass and glass products manufacturing
> > (8) Laundries
> > (9) Restaurant service areas
> > (10) Mechanical rooms with stockpiles up to 8 ft
> >
> > Statement of Problem and Substantiation for Public Input A new
> mechanical room by definition is a light hazard occupancy. The room is

> empty and the equipment is generally noncombustible. The AHJ likely 
> will not buy off that the room will not be used for storage.
> >
> > I also submitted Public Input No. 515-NFPA 13-2013 [ Section No. 
> > A.5.3.2
> ] that was rejected:
> > A.5.3.2
> > Ordinary hazard (Group 2) occupancies include occupancies having 
> > uses
> and conditions similar to the following:
> > ......
> > (31) Mechanical rooms with stockpiles up to 12 ft
> >
> > Committee Statement
> > Resolution: The definition of OH2 will drive the user to this 
> > occupancy
> hazard classification. This language is superfluous.
> >
> >
> > Tom Wellen
> >
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to