I agree with Chris on this one.  How can you be prosecuted for a code that
wasn't adopted by law in your state?  That would be like saying if you
design and install a system per an older legally adopted version of NFPA
13 and something happens you could be prosecuted for not following a more
strict rule from the latest edition of NFPA 13.  I try not to design with
antifreeze anymore but my state still allows it because they have adopted
the 2006 IBC and 07ed of NFPA 13.

-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Tom
Wellen
Sent: Thursday, June 04, 2015 7:42 AM
To: [email protected]
Subject: Re: Antifreeze systems

I'm hearing jurisdictions saying that the antifreeze ban does not apply to
them.  It is my understanding that NFPA intended for the new requirements
to apply regardless of what standard is in effect.

DO NOT INSTALL NEW ANTIFREEZE SYSTEMS AT THIS TIME.

Wait for the listed solution - but don't hold your breath.  Protect
yourself and protect your company.  The liability is too great to accept.
There are other options out there - dry pipe, preaction, wet in a heated
insulated attic, construct the attic out of noncombustible, limited
combustible, or fire treated wood.  If you proceed with the antifreeze
installation knowing or not knowing this hazard, you'll have nothing to
stand on in court. Many will testify against you. I'm not an attorney, but
if you proceed with that known hazard, it could be processed a criminal
matter. This is not worth ending up in the clink.

Tom Wellen








> On Jun 3, 2015, at 7:57 PM, Cahill, Christopher <[email protected]>
wrote:
>
> This is really a legal question which will vary by jurisdiction. NFPA
and various associations I believe agree with you.  I've even seen some
Fire Marshal's state they are retroactive. But I don't think it has been
legally tested.  I'm in a Hampton not a Holiday Inn Express but the way I
read MN law for example I don't see any way TIA's can be legally enforced
retroactively.  It has to go through the proper Code adoption procedures
as prescribed in law.  The biggest hang up is it has to be published
before notice to adopt is issued. If MN has just adopted a version of 13
(or anything else) and tomorrow a TIA comes out it's hard to argue the TIA
was out and part of the debate during the code adaption cycle that would
have begun 18 months ago.  Now if they are in the cycle to adopt they can
certainly add it rather late in the game as an amendment but then it's not
a TIA and it's not effective to previous version one would be working
under while the next version is in cycle.
>
> Chris Cahill, PE*
> Associate Fire Protection Engineer
> Burns & McDonnell
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
> *Registered in: MN
>
>
> Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work
> For
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of
> Travis Mack, SET
> Sent: Wednesday, June 03, 2015 6:42 PM
> To: [email protected]
> Subject: Re: Antifreeze systems
>
> If a TIA is issued, does that become retro-active to previous standards?
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> On 6/3/2015 4:41 PM, Forest Wilson wrote:
>>  It also depends on what edition of NFPA 13 has been adopted by your
jurisdiction.
>>
>>
>>
>>
>> Forest Wilson
>> Fire Sprinkler Contractor
>> PH: 937-736-0425
>> [email protected]
>>
>>
>>
>>
>>
>>
>> -----Original Message-----
>> From: rongreenman . <[email protected]>
>> To: sprinklerforum <[email protected]>
>> Sent: Wed, Jun 3, 2015 2:27 pm
>> Subject: Re: Antifreeze systems
>>
>>
>> The reason I have no hair is local jurisdictions thinking they have a
>> better insight into these problems than the committee because they
>> have a "special"
>> problem. I think they want the attic system because they're afraid of
>> firefighters falling through the roof. My solution has always been,
>> if this is a concern don't go on the roof. The shoe purpose of a 13R
>> is to afford residents more tenable escape time. If everyone is
>> standing on the sidewalk, surround and drown. Only my opinion though.
>>
>> On Wed, Jun 3, 2015 at 11:15 AM,
>> Parsley Consulting <
>> [email protected]> wrote:
>>
>>> Travis,
>>>     I
>> believe you have this correct, however, there's also a hook in the
>>> applicable
>> sections for 13R systems.
>>>     That link (if you scroll down), shows you the
>> page, you see the
>>> revised section 5.4.2 for 13R, and it notes that ares
>> needing freeze
>>> protection can use anti-freeze if it is a listed solution per
>> NFPA 13, and
>>> the installation of that sort of system is to be per NFPA 13.
>>>
>> Sounds like the AHJ for you Jay is stepping way out on a limb.  I
>>> don't know
>> if I'd do this sort of work with this sort of problem hanging
>>> over the
>> project, even if I did get the AHJ's instructions in writing with
>>> their
>> signature.  For me, one of the early seminars I attended included an
>>> advisory
>> that "How are you going to defend installing a system with
>>> anti-freeze when
>> you know it has this issue?"
>>>     Or maybe ask the AHJ if they're going to
>> defend you in court, and
>>> definitely get that in writing, since they're asking
>> you to install
>>> something outside of the adopted standard.
>>> *Ken Wagoner,
>> SET
>>> *Parsley Consulting***
>>> *350 West 9th Avenue, Suite 206
>>> *Escondido,
>> California 92025
>>> *****Phone 760-745-6181*
>>> Visit our website
>> <http://www.parsleyconsulting.com/>
>>>
>>> ***
>>> On 06/03/2015 10:52 AM,
>> Travis Mack, SET wrote:
>>>> Jay:
>>>>
>>>> The way I read that link is that you
>> can use AF listed for ESFR systems,
>>>> or you can use premix solutions in
>> "specific areas" of a new 13D
>>>> installation.  It doesn't say anywhere that it
>> is permitted in a 13R or 13
>>>> system based on that link.
>>>>
>>>> So, if you
>> are 13R, I don't see how it would comply with the
>>>> requirements.  But, maybe
>> I am reading something wrong.
>>>> Travis Mack, SET
>>>> MFP Design, LLC
>>>>
>> 2508 E Lodgepole Drive
>>>> Gilbert, AZ 85298
>>>> 480-505-9271
>>>> fax:
>> 866-430-6107
>>>> email:[email protected]
>>>>
>>>> http://www.mfpdesign.com
>>>>
>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>> Send large files
>> to us via: https://www.hightail.com/u/MFPDesign
>>>> On 6/3/2015 10:48 AM,
>> Jay Stough wrote:
>>>>> I have an AHJ that is telling me to install an
>> antifreeze system in a 13R
>>>>> attic.  They have an ordinance requiring attics
>> to be protected in 13R
>>>>> and
>>>>> 13D systems if deemed appropriate by the
>> fire marshal.  I was under the
>>>>> impression that after September of 2012 you
>> could not install new
>>>>> antifreeze systems without listed solution, which at
>> the present time is
>>>>> not available.  He is telling me that it just has to be
>> premixed.
>>>>>    When I go to the NFPA website, at
>>>>>
>>>>>
>> http://www.nfpa.org/safety-information/for-consumers/fire-and-safety-
>> e
>> quipment/home-fire-sprinklers/current-requirements-for-sprinkler-syst
>> e
>> ms-containing-antifreeze,
>>>>>
>> it appears that you can use premixed, even at the higher
concentrations.
>>>>>
>> Am I reading this correctly?
>>>>> *Jay Stough*
>>>>> NICET IV LAYOUT
>>>>>
>> NICET III ITM
>>>>> _______________________________________________
>>>>>
>> Sprinklerforum mailing list
>> [email protected]
>>>>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
>>>>
>> _______________________________________________
>>>> Sprinklerforum mailing
>> list
>>>> [email protected]
>>>>
>>>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
>>>>
>> _______________________________________________
>>> Sprinklerforum mailing
>> list
>>> [email protected]
>>>
>>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
>>
>>
>> --
>>
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering Technology Bates Technical College
>> 1101 So. Yakima Ave.
>> Tacoma, WA
>> 98405
>>
>> [email protected]
>>
>> http://www.bates.ctc.edu/fireprotection/
>>
>> 253.680.7346
>> 253.576.9700
>> (cell)
>>
>> Member:
>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>
>> They are happy men whose natures sort with their vocations. -Francis
>> Bacon, essayist, philosopher, and statesman (1561-1626)
>>
>> A problem well
>> stated is a problem half solved. -Charles F. Kettering, inventor and
>> engineer
>> (1876-1958)
>> _______________________________________________
>> Sprinklerforum
>> mailing
>> list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to