I agree with you, Bob.  Based on your description, EH1 in the chamber; OH2 
outside.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Friday, June 05, 2015 12:57 PM
To: [email protected]
Subject: Tire Vulcanizing Chamber

We're looking at a Tire Vulcanizing Chamber.  This is a self contained 
pressurized unit (80 psi) that is used to make retread tires.  The unit is 
about 24' long and 8' or so wide.  It is a cylinder.  13 allows tire 
manufacturing to be OH 2, but says that vulcanizing is EH1. Since the 
vulcanizing is a self contained steel unit can the overhead be protected per OH 
2 or does it need to be EH 1.  I'm leaning towards OH 2 since the process is in 
a self contained unit, but I would like other opinions.  The AHJ is good with 
whatever our decision is as long as we can back things up.

Thank you,

Bob Knight, CET III
208-318-3057
www.firebyknight.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to