Check the IBC (not sure of chapter and verse) I believe if you have less than 
20 sprinklers you can use the domestic supply and if it is capable of supplying 
the sprinkler demand plus the domestic flow.


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Tuesday, August 18, 2015 1:22 PM
To: [email protected]
Subject: 2" Residential Supply For Coolers

Quick question:
Is there anything that allows or disallows the use of a 2" domestic underground 
to supply sprinklers being added to (2) coolers in an existing building? From 
what I understand there are no other sprinklers in the building other than the 
ones they want added to the coolers. I assume the water demands for OH-2 plus 
hose for 60-90 minutes would still need to be met?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935