Ed,  yes ibc 903.3.8.3<http://3.3.8.3> provides that simultaneous demand be 
considered.

John Drucker - Mobile Email
[email protected]<mailto:[email protected]>
Cell/Text 732-904-6823


Ed Kramer <[email protected]> wrote:

Depending on what version of 13 you're using, you may need to add domestic
demand at the point of connection.  Ref 24.1.3.3 in the 2013.

Ed Kramer

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brian Harris
Sent: Tuesday, August 18, 2015 1:22 PM
To: [email protected]
Subject: 2" Residential Supply For Coolers

Quick question:
Is there anything that allows or disallows the use of a 2" domestic
underground to supply sprinklers being added to (2) coolers in an existing
building? From what I understand there are no other sprinklers in the
building other than the ones they want added to the coolers. I assume the
water demands for OH-2 plus hose for 60-90 minutes would still need to be
met?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to