Doesn't NFPA 14 require standpipe isolation valves? How can you individually 
isolate the standpipes in the scenario you describe. The valve that controls #1 
would also control #2&3. That doesn't seem to correlate with a requirement to 
be able to individually isolate each standpipe. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Aug 21, 2015, at 6:47 AM, Justin Petcosky <[email protected]> 
> wrote:
> 
> We have an engineer on a project that wants to run 2- Manuel wet standpipes 
> off the 1st floor sprinkler zone (which is supplied by a combination riser / 
> standpipe). So another words the combination riser comes from the basement of 
> the building which supplies the sprinkler zones. Then off the first floor 
> sprinkler zone the engineer wants to pick up two additional stairwells. I 
> know this isn't standard practice but please point me in the right direction 
> in NFPA 14.
> 
> 
> 
> 
> Justin Petcosky
> Vice President
> Petcosky and Sons
> Plumbing, HVAC and Fire Protection
> 421 Commerce Rd.
> Vestal, NY 13850
> www.petcosky-sons.com<http://www.petcosky-sons.com/>
> 607-797-0160 Ext.105
> [logo1]
> 
> 