Dewayne,

The IBC (if applicable) has possible exempt locations if approved by the AHJ...

2012 IBC...
[F] 903.3.1.1 NFPA 13 sprinkler systems. Where the provisions of this code 
require that a building or portion thereof be equipped throughout with an 
automatic sprinkler system in accordance with this section, sprinklers shall be 
installed throughout in accordance with NFPA 13 except as provided in Section 
903.3.1.1.1.
[F] 903.3.1.1.1 Exempt locations. Automatic sprinklers shall not be required in 
the following rooms or areas where such rooms or areas are protected with an 
approved automatic fire detection system, in accordance with Section 907.2, 
that will respond to visible or invisible particles of combustion. Sprinklers 
shall not be omitted from any room merely because it is damp, of 
fire-resistance-rated construction or contains electrical equipment.
1. Any room where the application of water, or flame and water, constitutes a 
serious life or fire hazard.
2. Any room or space where sprinklers are considered undesirable because of the 
nature of the contents, when approved by the fire code official.
3. Generator and transformer rooms separated from the remainder of the building 
by walls and floor/ceiling or roof/ceiling assemblies having a fire-resistance 
rating of not less than 2 hours.
4. In rooms or areas that are of noncombustible construction with wholly 
noncombustible contents.
5. Fire service access elevator machine rooms and machinery spaces.
6. Machine rooms and machinery spaces associated with occupant evacuation 
elevators designed in accordance with Section 3008.

I would focus on #2 and ask the question but I wouldn't expect to not have to 
sprinkler this space.  I think you would have a better chance convincing the 
AHJ if it was non-combustible construction but the plastic sheeting for walls 
is going to be a hurdle I would guess.

Thanks.

Reed



Reed A. Roisum, SET | Karges-Faulconbridge, Inc. | Senior Fire Protection 
Designer | Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dewayne Martinez
Sent: Friday, August 28, 2015 3:10 PM
To: [email protected]
Subject: Clean room sprinklers

We have a building with a ESFR sprinkler system installed that the owner has 
decided to install a portable clean room in.  The room itself has plastic 
sheeting for walls  and the ceiling is composed of air vents and acrylic 
panels.  No storage of combustibles is allowed inside and they use it to check 
LED panels for defects.  The room is about 12X20.  Is there any exception in 
NFPA 13 that would allow the omission of sprinklers from the room?  It just 
seems silly to require sprinklers in the room when you have 30ft rack storage 
next to it protected by the ESFR system.

Thanks,

Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to