Those system probably will blow the room apart based on the description of the 
lightweight materials used to create the rooms.

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mario Berrios
Sent: Sunday, August 30, 2015 1:36 PM
To: [email protected]
Subject: Re: Clean room sprinklers

Provide FM200;Inergen;refer to NFPA  2001 and 76.


Mario Berrios
[email protected]




-----Original Message-----
From: Russell & Carol Gregory <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Sat, Aug 29, 2015 12:04 am
Subject: RE: Clean room sprinklers


The basic answer is that it should be protected. We try to control a fire at 
its earliest stage of development.
It is unreasonable to wait until an ESFR head at the roof operates when this 
room and its contents will probably have been destroyed. The water damage may 
be excessive.
The smoke will have spread
around and coated stored material in adjacent racks.

Equate cost to install
against damage caused. 

There are a number of unknowns;
Value of room and
contents?
Type of goods stored in adjacent racks?
Is room moved regularly as
you said it was portable or is it temporary?
Can it be sited adjacent to a wall
or end of rack so a dropper can be run
down to the 2 - 4 sprinklers
needed?

Cheers,
Russell Gregory
Christchurch, New Zealand 


-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]]
On Behalf Of Dewayne
Martinez
Sent: Saturday, 29 August 2015 8:10 a.m.
To:
[email protected]
Subject: Clean room sprinklers

We
have a building with a ESFR sprinkler system installed that the owner has 
decided to install a portable clean room in.  The room itself has plastic 
sheeting for walls  and the ceiling is composed of air vents and acrylic 
panels.  No storage of combustibles is allowed inside and they use it to check 
LED panels for defects.  The room is about 12X20.  Is there any exception in 
NFPA 13 that would allow the omission of sprinklers from the room?  It just 
seems silly to require sprinklers in the room when you have 30ft rack storage 
next to it protected by the ESFR system.

Thanks,

Dewayne
_______________________________________________
Sprinklerforum
mailing
list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum
mailing
list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to