The basic answer is that it should be protected. We try to control a fire at
its earliest stage of development.
It is unreasonable to wait until an ESFR head at the roof operates when this
room and its contents will probably have been destroyed. The water damage
may be excessive.
The smoke will have spread around and coated stored material in adjacent
racks.

Equate cost to install against damage caused. 

There are a number of unknowns;
Value of room and contents?
Type of goods stored in adjacent racks?
Is room moved regularly as you said it was portable or is it temporary?
Can it be sited adjacent to a wall or end of rack so a dropper can be run
down to the 2 - 4 sprinklers needed?

Cheers,
Russell Gregory
Christchurch, New Zealand  

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Dewayne Martinez
Sent: Saturday, 29 August 2015 8:10 a.m.
To: [email protected]
Subject: Clean room sprinklers

We have a building with a ESFR sprinkler system installed that the owner has
decided to install a portable clean room in.  The room itself has plastic
sheeting for walls  and the ceiling is composed of air vents and acrylic
panels.  No storage of combustibles is allowed inside and they use it to
check LED panels for defects.  The room is about 12X20.  Is there any
exception in NFPA 13 that would allow the omission of sprinklers from the
room?  It just seems silly to require sprinklers in the room when you have
30ft rack storage next to it protected by the ESFR system.

Thanks,

Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to