Greg,

I am assuming this is being required due to the an IBC requirement.

Look at Section 404 and particularly 404.6 in the IBC (2009 ed)

This section only requires the closely spaced sprinklers and not Window 
sprinklers. The closely spaced sprinklers is given as an alternative to a 1 
hour rated wall. From your description the window sprinklers would not work 
anyway.

If there is a walkway in front of the glass, then the closely spaced sprinklers 
would be needed on both sides of the glass.

Good luck.

Best Regards,
Ken Holsopple

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Gregory Lindholm
Sent: Wednesday, September 02, 2015 7:26 AM
To: SprinklerFORUM <[email protected]>
Subject: Atrium

We have a new school that has a three story atrium, and the Architect is asking 
for us to protect the third floor glass with sprinklers place a maximum of 6' 
on center, and not more than 12" off the glass.
I originally assumed that we would use the Tyco Window Sprinklers, but the 
windows on this project has multiple horizontal mullions in the windows (4 or 
5).lowed with the Tyco heads.
I was thinking of just deigning it as a Water Curtain, with the regular heads 
at 6' on center, with 3 gpm per lineal foot.
Thoughts?

Greg Lindholm                                     