Found this IBC commentary online....

One of the basic premises of atrium requirements is that an engineered smoke 
control system combined with an automatic fire sprinkler system that is 
properly supervised provide an adequate alternative to the fire-resistance 
rating of a shaft enclosure. It is also recognized that some form of a boundary 
is required to assist the smoke control system in containing smoke to just the 
atrium area. The basic requirement, therefore, is that the atrium space be 
separated from adjacent areas by fire barriers and horizontal assemblies having 
a fire-resistance rating of at least 1 hour.

Also, openings in the wall are required to be protected, in accordance with 
Section 707.6. In accordance with Section 708.4, shafts are required to have a 
fire-resistance rating of at least 2 hours if connecting more than three 
stories, and 1 hour when connecting two or three stories. The basis for the 
1-hour requirement in Section 404.6 is that an automatic sprinkler system can 
be substituted for the 1 hour of fire resistance of a shaft enclosure. The 
allowance is consistent with the 1-hour fire-resistance-rating reduction 
permitted in high-rise buildings (see Section 403.2.1.2).

IN LIEU OF A 1-HOUR FIRE-RESISTANCE-RATED SEPARATION, Exception 1 allows 
adjacent spaces to be separated by glass walls where automatic sprinklers have 
been installed to protect the glass. The sprinklers are to be located so as to 
wet the entire surface of the glass wall. If there is a floor surface on each 
side of the wall, both sides of the glass must be protected. The glass must be 
in a gasketed frame such that the framing system can deflect without breaking 
the glass.

Although this exception does not address obstructions or other window 
treatments, consideration must be given to locating such items to avoid 
interference with the required sprinkler heads.

Without specific test evidence, curtain rods, traverse rods, curtains and 
draperies must be located at least 12 inches (305 mm) from the window surface 
[see Figure 404.6(1)]. Any doors through the required 1-hour fire barrier wall 
must be 3/4-hour rated in accordance with Table 715.4.

The sprinkler system required for Exception 1 is not intended to be a deluge 
system. Instead it is intended to protect the glazing material from breakage as 
a result of thermal shock. It is not necessary to activate all the sprinklers 
along the glazing material to provide such protection as long as the entire 
surface of the glazed panel is designed such that it can be wetted by the 
sprinkler system.

Exception 2 allows a glass-block wall assembly conforming to Section 2110. It 
is important to note that these glass-block assemblies do not require the 
sprinkler protection that is required by Exception 1.

Best Regards,
Ken Holsopple

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ken Holsopple
Sent: Thursday, September 03, 2015 9:54 AM
To: [email protected]
Subject: RE: Atrium

Mark and Geoff,

I agree that this in no way chalks up to the equivalent of a fire rated wall. 
(I am still under the impression that the only window sprinklers and the 
associated glass construction requirements are the only assembly out there that 
would be equivalent. It's been awhile since I have to deal with this.) But the 
mention of the smoke partition and the addition of "without Obstruction" makes 
me think in a different direction. 

The "without obstruction" means to me.....don't put a duct or soffit between 
the required closely spaced sprinklers and the glass. That is just my 
interpretation only. It is a prescribed alternative to a rated wall.

Without wanting to stray from what Greg originally ask asked, there is code 
basis for the request made of him from the design professional. The code is 
saying you can do this. I can't speak to the thought process behind allowing 
the alternative or what it will achieve. Maybe the glass is such a common 
feature that the authors thought it warranted an alternative, but didn't want 
to require the more expensive glass and window sprinkler configuration. I can't 
follow what may be implied, but I understand the concerns raised.

Just out of curiosity, does anyone know if this is still permitted in the newer 
additions of the IBC?

Best Regards,
Ken Holsopple

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, September 03, 2015 9:15 AM
To: [email protected]
Subject: RE: Atrium

I agree with Geoff. The problem remains the total wetting of the glass. This 
cannot be achieved with the horizontal mullions in  place. Moreover, can 
"entire surface of the glass" be wetted using standard sprinklers in a water 
curtain arrangement as opposed to listed window sprinklers?

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ken Holsopple
Sent: Wednesday, September 02, 2015 11:24 AM
To: [email protected]
Subject: RE: Atrium

Roland,

I don't disagree but.....

If Section 404.6  (see below) of the IBC prescribes the closely spaced 
sprinklers and the architect choses that instead of the other options listed to 
protect the atrium, then is it that big of a jump to apply Sections 8.15.4 and 
11.3.3 out of NFPA 13? (2007 edition.)

I only ask because the commentary in the 2007 handbook seems to allude that the 
requirement to provide the curtains is driven by the building code(s) and the 
NFPA 13 gives the how to.

404.6 Enclosure of atriums. Atrium spaces shall be separated from adjacent 
spaces by a I-hour fire barrier constructed in accordance with Section 707 or a 
horizontal assembly constructed in accordance with Section 712, or both.

Exceptions:
   1. A glass wall forming a smoke partition where automatic sprinklers are 
spaced 6 feet (1829 mm) or less along both sides of the separation wall, or on 
the room side only if there is not a walkway on the atrium side, and between 4 
inches and 12 inches (102 mm and 305
mm) away from the glass and designed so that the entire surface of the glass is 
wet upon activation of the sprinkler system without obstruction. The glass 
shall be installed in a gasketed frame so that the framing system deflects 
without breaking (loading) the glass before the sprinkler system operates.

    2. A glass-block wall assembly in accordance with Section
2110 and having a 3/4-hour fire protection rating.

     3. The adjacent spaces of any three floors of the atrium shall not be 
required to be separated from the atrium where such spaces are accounted for in 
the design of the smoke control system.

Funny how the IBC doesn't mention how many sprinklers are required to be 
calculated. Is a calc even necessary or is it implied that you go to NFPA 13 
for that?

Best Regards,
Ken Holsopple


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to