If I recall how it was explained to me, the testing concept, among other
things, is to buy time. If you can prove the heads are in acceptable
condition you can extend their usable life, but not in perpetuity. If the
heads are still serviceable you get another year and so on up to X years (I
forget but I think 10). This gives the owner a better ability to manage the
change out. If I owned a high rise I'd have started changing them out
earlier than the due date and come up with a plan acceptable to the FM to
stretch the cost out over several years. Failing to be proactive before the
expiration date, and hopefully finding that the heads were still
serviceable after the testing means I have a good start on replacement and
would immediately try to cut a deal with the AHJ to amortize the cost.
Maybe 20% per year for five years in exchange for no more tests.

And my opinion to your original question is that the property manager is
right, at least in this case. Unless there is some change in occupancy in
this high rise that would make one floor more likely to be impacted than
another. Perhaps a parking garage if it's by the sea or some other
potentially corrosive atmosphere. But otherwise what value is there in
having a full sampling from each floor? Why would the 12th floor of an
office building have more or less impact on the viability of the heads
installed there than say the 14th floor, or the 2nd, or the 23rd, or...?
But of course I may be missing something here.

On Mon, Oct 19, 2015 at 7:23 AM, Charles Thurston <[email protected]>
wrote:

> Hello Sprinklerforum,
>
>   Looking for a conses of how heads are picked to remove and send for
> testing. We have an AHJ that has been calling a floor an "area" for
> testing, Now that is being challenged by a property management co that
> claims it should be per:
>
> 3.6.4* Sprinkler System. For fire protection purposes, an integrated
> system of underground and overhead piping designed
> in accordance with fire protection engineering standards. The installation
> includes at least one automatic water supply that
> supplies one or more systems. The portion of the sprinkler system above
> ground is a network of specially sized or hydraulically
> designed piping installed in a building, structure, or area, generally
> overhead, and to which sprinklers are attached
> in a systematic pattern. Each system has a control valve located in the
> system riser or its supply piping. Each sprinkler system
> includes a device for actuating an alarm when the system is in operation.
> The system is usually activated by heat from a fire
> and discharges water over the fire area. [13, 2010]
>
> They are claiming that an "Area" is everything off that standpipe riser.
> Now if this is a high rise with floor controls off the standpipe, Does not
> each floor control make that floor a "system" or "Area" unto itself?
>
> --
> Best regards,
>  Charles                          mailto:[email protected]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to