The intent is to focus the sample so as to cover ALL the different potential environments that could impact the sprinkler operation. You obviously don’t want t pull a sample from just an air conditioned office space and not test any sprinklers from an exterior location like a loading dock. This concept of environment is identified in the Annex. I could have sworn we did a better job on this issue but it must have been a figment of my imagination. I do know the technical committee discussed this issue in great depth multiple cycles ago.
A.5.3.1.2 Within an environment, similar sidewall, upright, and pendent sprinklers produced by the same manufacturer could be considered part of the same sample, but additional sprinklers would be included within the sample if produced by a different manufacturer. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Oct 19, 2015, at 7:23 AM, Charles Thurston <[email protected]> wrote: > > Hello Sprinklerforum, > > Looking for a conses of how heads are picked to remove and send for testing. > We have an AHJ that has been calling a floor an "area" for testing, Now that > is being challenged by a property management co that claims it should be per: > > 3.6.4* Sprinkler System. For fire protection purposes, an integrated system > of underground and overhead piping designed > in accordance with fire protection engineering standards. The installation > includes at least one automatic water supply that > supplies one or more systems. The portion of the sprinkler system above > ground is a network of specially sized or hydraulically > designed piping installed in a building, structure, or area, generally > overhead, and to which sprinklers are attached > in a systematic pattern. Each system has a control valve located in the > system riser or its supply piping. Each sprinkler system > includes a device for actuating an alarm when the system is in operation. The > system is usually activated by heat from a fire > and discharges water over the fire area. [13, 2010] > > They are claiming that an "Area" is everything off that standpipe riser. Now > if this is a high rise with floor controls off the standpipe, Does not each > floor control make that floor a "system" or "Area" unto itself? > > -- > Best regards, > Charles mailto:[email protected] > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org