I like Bens logic to a point. But if I were the AHJ and you had two heads
fail in a 100k area rather than 2 fail in a 10k area I would be more
inclined to consider the former as a less dangerous scenario since the
latter suggest a tenfold higher failure rate. I'd be more inclined to
demand complete and mediate replacement of all heads in a building with a
2/10k failure rate than a 2/100k rate. The former sugAnd I obviously
invented the numbers to illustrate my point since we don't have real
numbers to work with.

On Monday, October 19, 2015, Ben Young <[email protected]> wrote:

> Its something of a gamble, because if any one of the heads fail in an
> 'area' all the heads in that area must be replaced.
> So if your area is the entire building, if any one head fails, you must
> replace them all.
> If you segregate by floor, and only two of the floors have heads that fail,
> you are only required to replace those floors (basically areas)
>
> So if you cheap out and want to test less heads and make very large areas,
> you may have to replace them all at the same time.
>
>
> Benjamin Young
>
> On Mon, Oct 19, 2015 at 11:50 AM, rongreenman . <[email protected]>
> wrote:
>
> > If I recall how it was explained to me, the testing concept, among other
> > things, is to buy time. If you can prove the heads are in acceptable
> > condition you can extend their usable life, but not in perpetuity. If the
> > heads are still serviceable you get another year and so on up to X years
> (I
> > forget but I think 10). This gives the owner a better ability to manage
> the
> > change out. If I owned a high rise I'd have started changing them out
> > earlier than the due date and come up with a plan acceptable to the FM to
> > stretch the cost out over several years. Failing to be proactive before
> the
> > expiration date, and hopefully finding that the heads were still
> > serviceable after the testing means I have a good start on replacement
> and
> > would immediately try to cut a deal with the AHJ to amortize the cost.
> > Maybe 20% per year for five years in exchange for no more tests.
> >
> > And my opinion to your original question is that the property manager is
> > right, at least in this case. Unless there is some change in occupancy in
> > this high rise that would make one floor more likely to be impacted than
> > another. Perhaps a parking garage if it's by the sea or some other
> > potentially corrosive atmosphere. But otherwise what value is there in
> > having a full sampling from each floor? Why would the 12th floor of an
> > office building have more or less impact on the viability of the heads
> > installed there than say the 14th floor, or the 2nd, or the 23rd, or...?
> > But of course I may be missing something here.
> >
> > On Mon, Oct 19, 2015 at 7:23 AM, Charles Thurston <[email protected]>
> > wrote:
> >
> > > Hello Sprinklerforum,
> > >
> > >   Looking for a conses of how heads are picked to remove and send for
> > > testing. We have an AHJ that has been calling a floor an "area" for
> > > testing, Now that is being challenged by a property management co that
> > > claims it should be per:
> > >
> > > 3.6.4* Sprinkler System. For fire protection purposes, an integrated
> > > system of underground and overhead piping designed
> > > in accordance with fire protection engineering standards. The
> > installation
> > > includes at least one automatic water supply that
> > > supplies one or more systems. The portion of the sprinkler system above
> > > ground is a network of specially sized or hydraulically
> > > designed piping installed in a building, structure, or area, generally
> > > overhead, and to which sprinklers are attached
> > > in a systematic pattern. Each system has a control valve located in the
> > > system riser or its supply piping. Each sprinkler system
> > > includes a device for actuating an alarm when the system is in
> operation.
> > > The system is usually activated by heat from a fire
> > > and discharges water over the fire area. [13, 2010]
> > >
> > > They are claiming that an "Area" is everything off that standpipe
> riser.
> > > Now if this is a high rise with floor controls off the standpipe, Does
> > not
> > > each floor control make that floor a "system" or "Area" unto itself?
> > >
> > > --
> > > Best regards,
> > >  Charles                          mailto:[email protected]
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >
> >
> >
> >
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering Technology
> > Bates Technical College
> > 1101 So. Yakima Ave.
> > Tacoma, WA 98405
> >
> > [email protected]
> >
> > http://www.bates.ctc.edu/fireprotection/
> >
> > 253.680.7346
> > 253.576.9700 (cell)
> >
> > Member:
> > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >
> > They are happy men whose natures sort with their vocations. -Francis
> Bacon,
> > essayist, philosopher, and statesman (1561-1626)
> >
> > A problem well stated is a problem half solved. -Charles F. Kettering,
> > inventor and engineer (1876-1958)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to