There are a couple of old buildings in Seattle that I know of with basement
only systems and no automatic water supplies (although equipped with
regular sprinklers) that must be pumped. I wonder if that was a common
practice back in the later part of the nineteenth and early twentieth
centuries. If so I can see a requirement for a FDC. Today I wonder how
often FDs pump sprinkler systems when they could be using those resources
(hydrants and pumpers) for their hoses.And if never (or even seldom) that
then leads to the question of why do we still have FDCs for sprinkler
systems. There are probably many very good reasons I'm not considering, I
don't and never have humped hoses, but I don't see any. And if there is no
reason for an FDC (particularly on a building that could qualify as 13R)
then why else would we need to have pipe that withstands 175 psi working
pressure (discounting combination systems that don't regulate the sprinkler
tie in to 130 psi or less). Then I would think PEX without the FDC would
work in 13R. Rhetorical questions of course as the FDC is required.

On Fri, Nov 6, 2015 at 10:49 AM, Pete Schwab <[email protected]> wrote:

> I am not aware of any Pex piping available for NFPA 13R. The Pex product
> cannot meet the 175 PSI requirement at higher temperatures. NFPA 13D allows
> 130 PSI at 120° which allows Pex.
> The only other plastic product listed (FM Approved) for fire protection
> that I am aware of is Aquatherm red pipe.
>
> http://www.aquatherm.com/aquatherm-red-pipe-polypropylene-sprinkler-piping
>
>
> Peter Schwab
> VP of Purchasing and Engineering technologies
>
> Wayne Automatic Fire Sprinklers Inc.
> 222 Capitol Court
> Ocoee, Fl 34761
>
> Mobile: (407) 468-8248
> Direct: (407) 877-5570
> Fax: (407) 656-8026
>
> www.waynefire.com
>
>
>
>
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Matt Grise
> Sent: Friday, November 06, 2015 10:30 AM
> To: [email protected]
> Subject: pex for 13R
>
> Has anyone developed pex piping for 13R applications? Is anyone pursuing
> that?
>
> Thanks!
>
> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.526.7443 cell
> www. AFPsprink.com
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to