Basement sprinklers, old buildings. Having your only escape route out of the 
basement be back up the stairs is not always comfortable. Can you imagine doing 
it in a pre-scba era?

I'd much rather pump it up from the outside.

Best

Bruce

> On Nov 6, 2015, at 11:31 AM, rongreenman . <[email protected]> wrote:
> 
> There are a couple of old buildings in Seattle that I know of with basement
> only systems and no automatic water supplies (although equipped with
> regular sprinklers) that must be pumped. I wonder if that was a common
> practice back in the later part of the nineteenth and early twentieth
> centuries. If so I can see a requirement for a FDC. Today I wonder how
> often FDs pump sprinkler systems when they could be using those resources
> (hydrants and pumpers) for their hoses.And if never (or even seldom) that
> then leads to the question of why do we still have FDCs for sprinkler
> systems. There are probably many very good reasons I'm not considering, I
> don't and never have humped hoses, but I don't see any. And if there is no
> reason for an FDC (particularly on a building that could qualify as 13R)
> then why else would we need to have pipe that withstands 175 psi working
> pressure (discounting combination systems that don't regulate the sprinkler
> tie in to 130 psi or less). Then I would think PEX without the FDC would
> work in 13R. Rhetorical questions of course as the FDC is required.
> 
>> On Fri, Nov 6, 2015 at 10:49 AM, Pete Schwab <[email protected]> wrote:
>> 
>> I am not aware of any Pex piping available for NFPA 13R. The Pex product
>> cannot meet the 175 PSI requirement at higher temperatures. NFPA 13D allows
>> 130 PSI at 120° which allows Pex.
>> The only other plastic product listed (FM Approved) for fire protection
>> that I am aware of is Aquatherm red pipe.
>> 
>> http://www.aquatherm.com/aquatherm-red-pipe-polypropylene-sprinkler-piping
>> 
>> 
>> Peter Schwab
>> VP of Purchasing and Engineering technologies
>> 
>> Wayne Automatic Fire Sprinklers Inc.
>> 222 Capitol Court
>> Ocoee, Fl 34761
>> 
>> Mobile: (407) 468-8248
>> Direct: (407) 877-5570
>> Fax: (407) 656-8026
>> 
>> www.waynefire.com
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]] On Behalf Of Matt Grise
>> Sent: Friday, November 06, 2015 10:30 AM
>> To: [email protected]
>> Subject: pex for 13R
>> 
>> Has anyone developed pex piping for 13R applications? Is anyone pursuing
>> that?
>> 
>> Thanks!
>> 
>> Matt Grisé PE*, LEED AP, NICET II
>> Sales Engineer
>> Alliance Fire Protection
>> 130 w 9th Ave.
>> North Kansas City, MO 64116
>> 
>> *Licensed in KS & MO
>> 
>> 913.888.0647 ph
>> 913.888.0618 f
>> 913.526.7443 cell
>> www. AFPsprink.com
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> 
> -- 
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> 
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to