Can't top Steve, but...

>From the handbook under 8.15.1.2.1.1:
The presence of openings in the ceiling, such as those for return air for a 
plenum, does not 
result in a perfunctory requirement for sprinklers in the concealed space. 
Evaluation of the size 
and number of openings in relation to the overall area of the ceiling is 
important. Examples of 
openings to plenum spaces are shown in Exhibit 8.34.

Ironically, Exhibit 8.34 labeled "Two Examples of Plenum Openings." shows two 
pictures of drop ceilings where the handbook is indicating sprinklers are not 
required above merely because of access.

In case you are wondering...purfunctory, synonymous for: superficial, careless, 
sketchy, offhand...

Duane Johnson, PE
Design Manager
Strickland Fire Protection
5113 Berwyn Road
College Park, MD 20740
301-474-1136 Office
301-455-0010 Cell


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark A. Sornsin, P.E.
Sent: Tuesday, November 10, 2015 2:37 PM
To: [email protected]
Subject: RE: Noncombustible concealed space

Ugh.  I've seen this on this forum before.  The AHJ is incorrect. Suspended 
ceiling tile is NOT the intent behind 'accessible'. How can the guy call it 
anything more than limited access? If this isn't limited access, what is?  I 
think the archives have better support for this; or someone else will chime in 
shortly.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Marc Walter, SET
Sent: Tuesday, November 10, 2015 1:31 PM
To: [email protected]
Subject: Noncombustible concealed space

I have a 1,300SF tenant finish project in a building that is post tension 
concrete. The tenant is dropping in a T-Bar grid ceiling throughout the space.



I have the existing piping dropping new pendents to the ceiling and removing 
the uprights. The AHJ has rejected the plans based on the removal of the 
uprights citing 8.15.1.2.1 and 8.15.1.2.2 (NFPA 13:2013).



His contention is that a T-Bar ceiling is a fully accessible space, and 
therefore requires sprinkler protection above. Anyone been hit with this before?



Marc Walter, SET

Sprinkler Design Services

780 6th Avenue

Seaside, OR  97138

(503) 956-4019



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to