Uhmm.. Bingo... What Steve said....

Rod at Rapid

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Tuesday, November 10, 2015 12:53 PM
To: [email protected]
Subject: RE: Noncombustible concealed space

Little known fact:  "Accessible" isn't defined in the building and there are 
only references to ADA in the California Codes.   The AHJ's observation is BS 
but I'll give them the benefit of the doubt and let's call this a teachable 
moment.   

"Dear Fire Official:

You have indicated that you believe the presence of removable ceiling tiles 
creates an accessible space above.   Accessibility as it is referred to in the 
building code is used in the context of moving people into a particular space.  
 It is an underlying premise of the building code that spaces are either 
occupiable or not; accessing a space and the requirements for that (ADA 
primarily) all infer that the space in question is occupiable and has a 
designated use and occupant load.   However, the noncombustible interstial 
space above a suspended t-bar ceiling does not meet those criteria:  there is 
no support or structure for storage or human occupancy and there is no 
dedicated use or occupancy classification as per the building code.  Therefore, 
such spaces meet the intent of NFPA 13, ยง8.15.1.2.2 and no sprinkler protection 
is required.

Our firm is contracted to design and install sprinklers per the adopted code 
and referenced standards.  In this case, it is widely accepted that such spaces 
are not considered occupied and sprinkler protection is not required.   If 
additional protection is required, I have to substantiate to the building owner 
why the additional costs are being incurred and I would greatly appreciate your 
assistance in that regard.   Please furnish any references or formal 
interpretations from NFPA or ICC or a recognized third party that you may have 
or on which your interpretation is based.  I look forward to reviewing this 
information with my client."




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Marc Walter, SET
Sent: Tuesday, November 10, 2015 11:31 AM
To: [email protected]
Subject: Noncombustible concealed space

I have a 1,300SF tenant finish project in a building that is post tension 
concrete. The tenant is dropping in a T-Bar grid ceiling throughout the space.

 

I have the existing piping dropping new pendents to the ceiling and removing 
the uprights. The AHJ has rejected the plans based on the removal of the 
uprights citing 8.15.1.2.1 and 8.15.1.2.2 (NFPA 13:2013).

 

His contention is that a T-Bar ceiling is a fully accessible space, and 
therefore requires sprinkler protection above. Anyone been hit with this 
before? 

 

Marc Walter, SET

Sprinkler Design Services

780 6th Avenue

Seaside, OR  97138

(503) 956-4019

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to