We are designing an apartment complex per NFPA 13 requirements. Is it permissible to install intermediate temperature sprinklers throughout all spaces (except those that would specifically require a high temp sprinkler due to other sections)?

The specific question arises because we have ordinary temperature sprinklers throughout most areas, and intermediate temp sprinklers in mechanical closets and laundry rooms in the dwelling units. The AHJ states that since the areas (mech closets and laundry areas in the dwelling units) are conditioned spaces, that we must use ordinary temperature rated sprinklers. He states that Table 8.3.2.5(c) over-rides the flexibility provided by 8.3.2.1 which allows ordinary or intermediate temp sprinklers throughout buildings.

This has been common practice to install the intermediate temp sprinklers in these areas. This is the first time that this plan reviewer has ever brought this up. Some contractors in this area are moving toward intermediate temp sprinklers throughout in residential areas for various reasons.

--