Opinions please
NFPA #13 2013 ed section 8.15.11 Electrical Equipment. Room is used as a server room, only the server and the UPS are in the room, the room is 2 hour fire rated. Section 8.15.11.3 Sprinklers shall not be required in electrical equipment room where all of the following conditions are met: (1) Room is dedicated to electrical equipment only yes (2) Only dry-type electrical equipment is used. Yes (3) Electrical equipment is installed in a 2 hour rated enclosure including protection of penetrations yes (4) No combustibles storage is permitted to be stored in the room. yes Based on this can the sprinkler heads be eliminated from this room? Would still have to get it by the AHJ. Thank you James Crawford Phaser Fire Protection Ltd. Phone 604-888-0318 Fax 604-888-4732 Cel 604-790-0938 Email [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org