Roland. Freezer warehouse protection in a server room??????? Cryogenic cooling maybe?????? I see no advantage to the added complexity and just a lot of added cost in installation and maintenance, apart from the increased risk of unreliability with a DIPA. If, as you say, loss of data is the concern wet pipe with offsite backup. If continuity of business (of if a supercomputer for a server room 😵) then a SIPA with pipe integrity monitoring (12oz air) would be advisable. Or maybe if this is all so critical you can build a back-up server room with wet sprinks. Savings in not installing SIPA and its associated maintenance cost (and unreliability if not maintained properly–amazing how many "professionals" don't understand pre-action) and the cost of two hour rooms might offset the duplicate computers in another location within the facility.
And of course, on a seperate topic, there's the no storage in a room with a door clause that means there will be storage. Testing a halon with SIPA back-up once. Found four wonder gas bottles in a bank and removed the solenoid releases for the test. Fortunately the tech needed a tool and so I just wandered around a little. Found some big pressure hosing going into a closet. Looked in the closet and it was full pf empty cardboard boxes. Pulled some out and found a fifth halon bottle. lucky day. On Thu, Nov 19, 2015 at 12:08 PM, David Blackwell < [email protected]> wrote: > Don't forget about (2010) NFPA 13 21.14 Protection of Information > Technology Equipment... > > Respectfully, > > > David W. S. Blackwell, II, PE, CFPE, CFI I > Chief Engineer > Office of State Fire Marshal > SC Department of Labor, Licensing, & Regulation, 141 Monticello Trail, > Columbia, SC 29203 > Telephone: 803.896.9800 [Office] 803.896.9833 [Direct] > Fax: 803.896.9806 [Office] > Email: [email protected] > Website: http://www.scfiremarshal.llronline.com/ > > > Please note that you can find a lot of information on our website at > http://www.scfiremarshal.llronline.com/ including contact information, > current events, laws, regulations, policies, forms, procedures, and links > to other website resources for further information. > > -----Original Message----- > From: Sprinklerforum [mailto: > [email protected]] On Behalf Of Roland > Huggins > Sent: Thursday, November 19, 2015 3:00 PM > To: [email protected] > Subject: Re: Electrical Equipment room > > *** SCDLLR NOTICE *** This email is from an external email address. Please > use caution when deciding whether to open any attachments or when clicking > links inside the email. > > BULLSEYE > > Sounds like someone is doing the A/E dance. Not the first time one has > attempted to say this means equipment that uses electricity. > > If the value of the data or continuity of business warrants it, suggest > they do a double interlock preaction system. > > Roland Huggins, PE - VP Engineering > American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives > Dallas, TX > http://www.firesprinkler.org <http://www.firesprinkler.org/> > > > > > > > On Nov 19, 2015, at 11:47 AM, <[email protected]> < > [email protected]> wrote: > > > > A server and a UPS is not an electrical room nor considered "electrical > equipment". > > > > "Electrical Rooms" house Transformers, MCCs and Switchgear. The clue is > the mention of dry type equipment. You haven't seen any oil cooled > computers have you? > > > > So technically this doesn't apply but it depends on what you convince > the AHJ it means. > > > > > > If they are adamant about not putting sprinklers in the room, the better > argument is found in the Fire Code in 903.3.1.1.1 EXEMPT LOCATIONS where > you could use exemption (2)"Any room or space where sprinklers are > considered undesirable because of the nature of the contents, when approved > by the fire code official." Now the room will require the installation of > smoke detectors if you omit the sprinklers. Run that by the AHJ and see if > it flies. > > > > > > > > Craig L. Prahl > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) A problem well stated is a problem half solved. -Charles F. Kettering, inventor and engineer (1876-1958) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org