Roland. Freezer warehouse protection in a server room??????? Cryogenic
cooling maybe?????? I see no advantage to the added complexity and just a
lot of added cost in installation and maintenance, apart from the increased
risk of unreliability with a DIPA. If, as you say, loss of data is the
concern wet pipe with offsite backup. If continuity of business (of if a
supercomputer for a server room 😵) then a SIPA with pipe integrity
monitoring (12oz air) would be advisable. Or maybe if this is all so
critical you can build a back-up server room with wet sprinks. Savings in
not installing SIPA and its associated maintenance cost (and unreliability
if not maintained properly–amazing how many "professionals" don't
understand pre-action) and the cost of two hour rooms might offset the
duplicate computers in another location within the facility.

And of course, on a seperate topic, there's the no storage in a room with a
door clause that means there will be storage. Testing a halon with SIPA
back-up once. Found four wonder gas bottles in a bank and removed the
solenoid releases for the test. Fortunately the tech needed a tool and so I
just wandered around a little. Found some big pressure hosing going into a
closet. Looked in the closet and it was full pf empty cardboard boxes.
Pulled some out and found a fifth halon bottle. lucky day.

On Thu, Nov 19, 2015 at 12:08 PM, David Blackwell <
[email protected]> wrote:

> Don't forget about (2010) NFPA 13 21.14 Protection of Information
> Technology Equipment...
>
> Respectfully,
>
>
> David W. S. Blackwell, II, PE, CFPE, CFI I
> Chief Engineer
> Office of State Fire Marshal
> SC Department of Labor, Licensing, & Regulation, 141 Monticello Trail,
> Columbia, SC 29203
> Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
> Fax: 803.896.9806 [Office]
> Email:   [email protected]
> Website:  http://www.scfiremarshal.llronline.com/
>
>
> Please note that you can find a lot of information on our website at
> http://www.scfiremarshal.llronline.com/ including contact information,
> current events, laws, regulations, policies, forms, procedures, and links
> to other website resources for further information.
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Roland
> Huggins
> Sent: Thursday, November 19, 2015 3:00 PM
> To: [email protected]
> Subject: Re: Electrical Equipment room
>
> *** SCDLLR NOTICE *** This email is from an external email address. Please
> use caution when deciding whether to open any attachments or when clicking
> links inside the email.
>
> BULLSEYE
>
> Sounds like someone is doing the A/E dance.  Not the first time one has
> attempted to say this means equipment that uses electricity.
>
> If the value of the data or continuity of business warrants it, suggest
> they do a double interlock preaction system.
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org <http://www.firesprinkler.org/>
>
>
>
>
>
> > On Nov 19, 2015, at 11:47 AM, <[email protected]> <
> [email protected]> wrote:
> >
> > A server and a UPS is not an electrical room nor considered "electrical
> equipment".
> >
> > "Electrical Rooms" house Transformers, MCCs and Switchgear.  The clue is
> the mention of dry type equipment.   You haven't seen any oil cooled
> computers have you?
> >
> > So technically this doesn't apply but it depends on what you convince
> the AHJ it means.
> >
> >
> > If they are adamant about not putting sprinklers in the room, the better
> argument is found in the Fire Code in 903.3.1.1.1 EXEMPT LOCATIONS where
> you could use exemption (2)"Any room or space where sprinklers are
> considered undesirable because of the nature of the contents, when approved
> by the fire code official."  Now the room will require the installation of
> smoke detectors if you omit the sprinklers. Run that by the AHJ and see if
> it flies.
> >
> >
> >
> > Craig L. Prahl
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to